Can tap conductors terminate in a main lug only panel or does the panel require a main circuit breaker?

Most, if not all taps must end in an overcurrent device.

If you are stuck with a MLO panel you may have to install a fused disconnect or a single breaker enclosure outside the panel.
 

cppoly

Senior Member
Location
New York
Curious about how to interpret this:

For 10' tap 240.21(B)(1), the ampacity of the tap conductors is to be "not less than the rating of the device supplied by the tap conductors or not less than the rating of the overcurrent protective device at the termination of the tap conductors."

Here is says device or OCPD.

Yet for 25' tap, 240.21(B)(2) the ampacity of the tap conductors is "the ampacity of the tap conductors is not less than one-third of the rating of the overcurrent device protecting the feeder conductors."

For 10' tap it says device or OCPD and in 25' tap it only says OCPD... interesting
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Even if you had a 10' tap you would still need to comply with this:

408.36 Overcurrent Protection. In addition to the re-
quirement of 408.30, a panelboard shall be protected by an
overcurrent protective device having a rating not greater
than that of the panelboard. This overcurrent protective de-
vice shall be located within or at any point on the supply
side of the panelboard.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I think you will see a bit of a change in 2014

(1) Taps Not over 3 m (10 ft) Long. If the length of the
tap conductors does not exceed 3 m (10 ft) and the tap
conductors comply with all of the following:
(1) The ampacity of the tap conductors is
a. Not less than the combined calculated loads on the
circuits supplied by the tap conductors, and
b. Not less than the rating of the equipment containing
an overcurrent
device(s) supplied by the tap conductors
or not less than the rating of the overcurrent
protective device at the termination of the tap conductors.
Exception to b: Where listed equipment, such as a surge
protective device(s) [SPD(s)], is provided with specific instructions
on minimum conductor sizing, the ampacity of
the tap conductors supplying that equipment shall be permitted
to be determined based on the manufacturer?s
instructions.




(2) Taps Not over 7.5 m (25 ft) Long. Where the length of
the tap conductors does not exceed 7.5 m (25 ft) and the tap
conductors comply with all the following:
(1) The ampacity of the tap conductors is not less than
one-third of the rating of the overcurrent device protecting
the feeder conductors.
(2) The tap conductors terminate in a single circuit breaker
or a single set of fuses that limit the load to the ampacity
of the tap conductors. This device shall be permitted
to supply any number of additional overcurrent devices
on its load side.
(3) The tap conductors are protected from physical damage
by being enclosed in an approved raceway or by other
approved means.
 
Last edited:

Smart $

Esteemed Member
Location
Ohio
I edited the post and highlighted the changes-- sorry

Under 2014's 10' tap rule, the ampacity of the conductors must not be less than the MLO panel's rating, but...

The MLO panel is still required to be protected per 408.36. That protection would be the feeder OCPD. This makes the whole issue of taps to supply an MLO panel moot.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
The change for 2014 is a problem when you are using a fusible disconnect at the load end of the tap conductors. The tap conductor must have an ampacity equal to the rating of the disconnect itself, and not of the fuses that are installed in the disconnect. The wording needs some tweaking.
 

Smart $

Esteemed Member
Location
Ohio
The change for 2014 is a problem when you are using a fusible disconnect at the load end of the tap conductors. The tap conductor must have an ampacity equal to the rating of the disconnect itself, and not of the fuses that are installed in the disconnect. The wording needs some tweaking.
Is that because the switch is ahead of the fusing? That is, the tap conductors do not directly terminate to the OCPD even though it is integral with the device.
 

kwired

Electron manager
Location
NE Nebraska
Under 2014's 10' tap rule, the ampacity of the conductors must not be less than the MLO panel's rating, but...

The MLO panel is still required to be protected per 408.36. That protection would be the feeder OCPD. This makes the whole issue of taps to supply an MLO panel moot.

In a recent thread this was brought up where you would run into a device that could be used under this section - one example that was brought up was switchboards without a single main, as they would not necessarily require the same overcurrent protection of the bus as a panelboard would. (This all from memory, go ahead and shoot holes in it if you see fit)
 

Smart $

Esteemed Member
Location
Ohio
In a recent thread this was brought up where you would run into a device that could be used under this section - one example that was brought up was switchboards without a single main, as they would not necessarily require the same overcurrent protection of the bus as a panelboard would. (This all from memory, go ahead and shoot holes in it if you see fit)
No holes to shoot. I may have been the one to bring that up.. ;)
 

kwired

Electron manager
Location
NE Nebraska
quote_icon.png
Originally Posted by Smart $

Is that because the switch is ahead of the fusing? That is, the tap conductors do not directly terminate to the OCPD even though it is integral with the device.
That is how the words read to me.


That is how the words read, something tells me that is not the intent though.

I would think a typical fused disconnect is considered an overcurrent device just like a circuit breaker is, even though it is an assembly of two major components, it is sold as a single listed unit. A fuseholder with a separate adjacent disconnecting means as is mentioned a time or two in the NEC is likely an example of where this "device" comes to play. JMO.
 

jap

Senior Member
Occupation
Electrician
I would think that it would be because there's always the chance that a larger fuse could be installed in the disconnect in some cases, thus "Overfusing" the Tap Conductor.

For example a 125 amp tap to a 125 amp fuse installed in a 200 Amp Rated Disconnect or a 225 Amp tap to a 225 Amp Fuse installed in a 400 Amp Disconnect.
 

Smart $

Esteemed Member
Location
Ohio
I would think that it would be because there's always the chance that a larger fuse could be installed in the disconnect in some cases, thus "Overfusing" the Tap Conductor.

For example a 125 amp tap to a 125 amp fuse installed in a 200 Amp Rated Disconnect or a 225 Amp tap to a 225 Amp Fuse installed in a 400 Amp Disconnect.
I don't agree. You'd likely have that situation even if it was just fusing and no switch.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
quote_icon.png
Originally Posted by Smart $

Is that because the switch is ahead of the fusing? That is, the tap conductors do not directly terminate to the OCPD even though it is integral with the device.


That is how the words read, something tells me that is not the intent though.

I would think a typical fused disconnect is considered an overcurrent device just like a circuit breaker is, even though it is an assembly of two major components, it is sold as a single listed unit. A fuseholder with a separate adjacent disconnecting means as is mentioned a time or two in the NEC is likely an example of where this "device" comes to play. JMO.
Not sure about that...the previous code said that the 10' tap conductor had to have an ampacity not less than the rating of the device, but did not require that the device contain an OCPD. The intent of the change is to require that the tap conductor terminate on an OCPD, or at equipment that contains an OCPD. The rule clearly requires that the tap conductor have an ampacity of not less than the rating of the equipment that contains an OCPD. The equipment that contains the OCPD is the disconnect itself and the fuse is the "contained OCPD".
2014 b. Not less than the rating of the equipment containing an overcurrent device(s) supplied by the tap conductors or not less than the rating of the overcurrent protective device at the termination of the tap conductors.
2011 b. Not less than the rating of the device supplied by the tap conductors or not less than the rating of the overcurrent protective device at the termination of the tap conductors.
 