I am a little confused..I am going to install wiring for a couple of 4HP 208V 3 phase hermetic compressors.(Separate units)
**Branch circuit wiring is RLA & 125% No problem
**OCPD is 175% or 225% if needed No problem
**But the disconnect - 440.12 says 115% - However Since 440.12(A)(2) says if HP is not listed in table 430-250, then the next higher value must be used. That would be 5 HP - OK, table 430-251(B) says the disconnect required ampere rating must be 105.8 amps.
A Siemens 60 amp disconnect is rated for 7.5 HP at 208 V - I'm assuming that since the 60A disconnect is rated for 7.5 HP, then it is technically rated for > 105.8 Amps for LRC? It's hard to believe that I need to go to a 200Amp disconnect?
Am I reading this right?