4 Wire Delta-Delta Center Tapped Connection Analysis
Thanks for your quick response!
Actually this is not a homework or test. I attended a seminar last week and this connection was presented. I found an example from a paper of General Electric and I took the loads from it. In the paper, they just present the formulas to size the transformers. So this is me trying to analyze the connection.
I have an error on the original diagram. The largest transformer should be 35KVA, not 45KVA. I attached it again with the correction.
What I know is this....
I calculated the current on the single phase load by dividing 45KVA by 240V and i got 187.5A. I also calculated the line current on the three phase load 15KVA / 1.732*240V and I got 36.1A. Having this, this should be the values of ia, ib and ic.
ia = 187.5 + 36.1 = 223.6A
ib = 187.5 + 36.1 = 223.6A
ic = 36.1A
ia' = 20KVA/240V = 83.33A (Transformer capacity divided by it's voltage)
ib' = 35KVA/240V = 145.83A (Transformer capacity divided by it's voltage)
ic' = 20KVA/240V = 83.33A (Transformer capacity divided by it's voltage)
Here are my questions....
1) If you make a KCL on X3 of each transfomer, you can add or substract the currents and they doesn't match. For example, let's make a KCL on X3 of T3. -ic' - ia' + ic = 0. If I want to obtain ic, it should be: ic = ic' + ia' = 166.67A or 0A if you change the direction of the currents. Analyzing the circuit from the load, I obtained that ic = 36.1A. I don't know if you have to add or substract those currents as phasors instead of just the magnitude.
2) If you have to add them (currents) as phasors instead of just the magnitude, what should be their angles??
If you need more information please let me know.
Thanks once again;
Ismael