Conduit fill with XHHW with #6-4 conductor cable, and THANKS!

Status
Not open for further replies.

JasonMT

Member
Location
United States
Im trying to figure out the correct conduit size (schedual 40 PVC) to use with a 4 conductor cable. The cable contains 4 #6 XHHW-2 conductors. I know that Nec says: A multiconductor cable or flexible cord of two or more conductors shall be treated as a single conductor for calculating percentage conduit fill area. I measured the cable, It measures 5/8 of a inch, and is perfectly round. I used the formula, A= 3.14* R squared. Which comes out to be 1.23 inches squared. Chapter 9 tables tell me schedual 40 PVC with one wire 53%. So I used this column which I came out with 2 inch PVC= 1.744 In. Sq.. 1 1/2 = 1.052 In. Sq.. 1.23 In. Sq. is between these 2 numbers. So I should use 2 inch sch 40 PVC. Is This correct?

I also recently passed my state Journeyman test recently. I used this site for studying for the exam. I had alot of questions. That alot of people helped me with. I just want to say thank you for your help.
 

JasonMT

Member
Location
United States
I work in substations for a Utility. The Nec does not apply there. I try to use it on every thing I do there. The cable is installed in trend way. Its what they used for every thing. The trend way tends to fill up with water. So I cant convert it with a J-Box. I have to pull it through the trendway then through a pipe that plugs into the trend way, to the first Box that serve the yard lts.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
Are you using 5/8" as the radius rather than the diameter in the area formula? A diameter of 5/8 inches will not give you more than 1 sq. in. of area!
 

JasonMT

Member
Location
United States
Now when i recalculate my mistake, it says I can use a 1" pipe. The cable is pretty tight going through a 1" pipe. Plus I have to use a blanket heater to bend it around the concrete going up to the first lt box. Theres no way 1 inch pvc will hold its form after those bends.
 

ActionDave

Chief Moderator
Staff member
Location
Durango, CO, 10 h 20 min from the winged horses.
Occupation
Licensed Electrician
I work in substations for a Utility. The Nec does not apply there. I try to use it on every thing I do there. The cable is installed in trend way. Its what they used for every thing. The trend way tends to fill up with water. So I cant convert it with a J-Box. I have to pull it through the trendway then through a pipe that plugs into the trend way, to the first Box that serve the yard lts.
Go forth and boldly calculate away then.

I try to avoid cable in conduit calculations by never doing something where I need to do them.
 