According to the NEC (2014), "285.5 An SPD shall be a listed device."
My first point of confusion is the scope. Since article 285's scope covers "surge-protective devices (SPDs) permanently installed on premises wiring systems of 1000 volts or less," would someone clarify whether this includes industrial panels? I know that the definitions in Article 100 seem to distinguish industrial panels from premises wiring, but there does seem to be some overlap. On the other hand, in my thinking, the most obvious understanding of premises wiring would be power/signal wiring inside and outside a building as opposed to that which is inside an industrial panel. Is that right, or is it an over-simplification?
My second problem relates to interpreting what UL might mean about listing on its own website concerning SPDs. Regarding SPDs of type 1, 2, and 3, UL1449 indicates that "These devices are listed." However, I have in my possession a Type 2 SPD that is labeled with the "Recognized" symbol instead of the "Listed" symbol, and I have found at least two more from other manufacturers also selling in the U.S. that also list both of their Type 2 devices as UL-Recognized and not listed. So my question is this: what does UL1449 mean when it states that Type 2 SPDs "are listed," given the fact that I can get several SPDs of that type which indicate that they are merely recognized?
What all this boils down to is whether it matters if I use an SPD that is labeled as recognized in an industrial panel. Common sense tells me yes, but I figured I should run these questions through a multitude of counselors first.
Kind regards,
The Shackled Designer
My first point of confusion is the scope. Since article 285's scope covers "surge-protective devices (SPDs) permanently installed on premises wiring systems of 1000 volts or less," would someone clarify whether this includes industrial panels? I know that the definitions in Article 100 seem to distinguish industrial panels from premises wiring, but there does seem to be some overlap. On the other hand, in my thinking, the most obvious understanding of premises wiring would be power/signal wiring inside and outside a building as opposed to that which is inside an industrial panel. Is that right, or is it an over-simplification?
My second problem relates to interpreting what UL might mean about listing on its own website concerning SPDs. Regarding SPDs of type 1, 2, and 3, UL1449 indicates that "These devices are listed." However, I have in my possession a Type 2 SPD that is labeled with the "Recognized" symbol instead of the "Listed" symbol, and I have found at least two more from other manufacturers also selling in the U.S. that also list both of their Type 2 devices as UL-Recognized and not listed. So my question is this: what does UL1449 mean when it states that Type 2 SPDs "are listed," given the fact that I can get several SPDs of that type which indicate that they are merely recognized?
What all this boils down to is whether it matters if I use an SPD that is labeled as recognized in an industrial panel. Common sense tells me yes, but I figured I should run these questions through a multitude of counselors first.