rlundsrud
Senior Member
- Location
- chicago, il, USA
I have to ask the OP, did you actually see this happen in person. Ifor you were told this happened by someone you consider to be reliable and in order to back that individual up are relaying the story as though you witnessed it is a formula for confusion. It is very much human nature to do this, so when I ask this it is not out of animosity nor is it meant to be accusing. I only ask as these events seem so very improbable that it seems to defy any other logic. A fundamental premise in being able to provide advice or assistance is to know all the factors that have occured. Information is always tainted when it is passed from one person to another. Please accept my apologies for casting doubts, I wish only to know the actual facts. If this story was relayed to you by someone please let us know. I don't doubt that you have worked on resolving this issue with all due diligence, I just can't believe that this keeps occurring given the the events as told. The breakers going to the off position and not the tripped position is especially difficult to reason out. I certainly would have taken a few breakers from one of the other units that have worked just fine and swapped them to see what happened. It eliminates geography and they are know good devices under the same relative working conditions. That would be my go to move.
Bob
Bob