Does using 3R equipment and raintight wiring methods qualify as protection from possible leaks from water pipes?
Yes IMO.Does using 3R equipment and raintight wiring methods qualify as protection from possible leaks from water pipes?
At first I thought you actually needed a drip shield. But that is not what the code says. You only need protection from damage from condensation. So I agree with the others. The pipes still need to be more than 6 feet above the top of the panel, but you can take credit for the 3R rating as providing the required protection.
There is no requirement to keep foreign piping above a lighting relay panel. You don't need to put it within a 3R enclosure.There is a lighting relay panel which doesn't come in 3R so I am going to put it in a 3R cabinet which brings up other challenges.
There is no requirement to keep foreign piping above a lighting relay panel. You don't need to put it within a 3R enclosure.
Then we must take care of what we call it. I think it meets the article 100 definition of "panelboard." That would bring into play the requirement for dedicated equipment space. If the panel only had relays to control lighting, then I think it would not meet the definition of "panelboard," and the dedicated equipment space would not apply.Charles, what if its a lighting relay panel that has CB's with the relays built on?