I have noticed differing minimum motor circuit conductor sizes (#10 & #8) from various sources for a 20HP 460V 3 phase motor. I would size at #8, assuming the overcurrent protection limitations of 240.4(D) [as noted in table 310.15(B)(16)] apply for motors also. Apparently, some are either unaware of these limitations or believe they do not apply to motors. I cannot find any evidence to support the notion that 240.4(D) does not apply for motors when using #10 AWG. Appreciate any help.