Under ground conductor ampacity rating.

Status
Not open for further replies.

twsteed

Member
Location
Douglas, Wyoming
My question involves 2/0 aluminum USE, 75 degree C wire and terminations, triplex cable. The conductors originate and terminate outside of a building. If I use table 310.15(B)(2)(a) and an underground temperature of 59 degrees F, can I increase the ampacity and OCP of the conductor?
Less than 10 feet of conductor above grade on either end. 1.15 x135=155 amps.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
what about the equipment at point of termination ? What temperature termination will that allow (ref: 110.14) ?
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
Less than ten feet above grade at either end, OK. But what is the length underground?
The exception I am thinking of allows 10' or 10% whichever is smaller.
 

twsteed

Member
Location
Douglas, Wyoming
Do not know of any 10 percent length exception, both ends would be about six feet long and about a sixty foot long underground length. The terminations on both ends are rated for 75 degrees C.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
110.14 is going to be the limiting factor. Regardless of the adjusted amapcity of the conductor, the allowed ampacity can not exceed the provisions given in 110.14, in the case of 20 AL that would be 135 amps.
240.4(B) would allow you a 150 amp overcurrent device but your calculated load could not exceed 135 amps.
 

twsteed

Member
Location
Douglas, Wyoming
Gentlemen, thank you for your input, but I respectfullydisagree. 310.15(B) allows for the" temperature correction and adjustmentfactors shall be permitted to be applied to the to the ampacity for thetemperature rating of the conductor".
I am using the 75 degree C column in the "AmbientTemperature Correction " table, 310.15(B)(2)(a). according to the table, Iam not exceeding the 75 degree limitation.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
310.15(B)(16) shows the allowable ampacity of 2/0 AL at 135 amps.
Adjusting for ambient my well change the ampacity of the conductor, and 110.14 limits you to that an ampacity rating for 75? terminations, IMO.
Hopefully others will have an opinion also.
 