140822-0926 EDT
GITRDUN:
Last night I stopped by the shop and looked at our 3-96 VF-3. In the manual all the solenoid controlling items are drawn as a conventional electromagnetic relays. But looking at the IO board it is clear some are ordinary relays and others are solid state switches. I could not read the part numbers.
These relays switch the solenoids from one of the 115 V secondaries on the output of the 3 phase transformer. I believe these are on the output side of the 3 pole 115 V circuit breaker. You did not mention the optical coupler failing. Thus, the circuit where the failure occurs is the SSR in series with the solenoid supplied by the 115 V source. No part of this circuit should be grounded (connected to chassis).
There is no high current path here. The maximum current is defined by the solenoid. This impedance will be low if the solenoid gets stuck or is shorted, then a higher than steady state current will flow. Otherwise not more than V/Zclosed currrent should flow thru the SSR.
If the SSR shorts, then the solenoid is continuously energized. If the SSR fails open, then the solenoid never closes. That the circuit breaker trips implies high current. How is high current generated without other failures?
I also tried a very simple experiment of monitoring the 3 phase 115 V output with a Fluke 27 in min/max mode at power disconnect, i.e., powering down with the off pushbutton. Less than a volt variation and that is well within the short normal line voltage variation. Thus, upon a sample of one I did not see a likely switching transient problem.
There is nothing so far that seems to make sense relative to the cause of your failures.
Do these machines have any external equipment connected to them? Computers, robots, etc?
.
GITRDUN:
Last night I stopped by the shop and looked at our 3-96 VF-3. In the manual all the solenoid controlling items are drawn as a conventional electromagnetic relays. But looking at the IO board it is clear some are ordinary relays and others are solid state switches. I could not read the part numbers.
These relays switch the solenoids from one of the 115 V secondaries on the output of the 3 phase transformer. I believe these are on the output side of the 3 pole 115 V circuit breaker. You did not mention the optical coupler failing. Thus, the circuit where the failure occurs is the SSR in series with the solenoid supplied by the 115 V source. No part of this circuit should be grounded (connected to chassis).
There is no high current path here. The maximum current is defined by the solenoid. This impedance will be low if the solenoid gets stuck or is shorted, then a higher than steady state current will flow. Otherwise not more than V/Zclosed currrent should flow thru the SSR.
If the SSR shorts, then the solenoid is continuously energized. If the SSR fails open, then the solenoid never closes. That the circuit breaker trips implies high current. How is high current generated without other failures?
I also tried a very simple experiment of monitoring the 3 phase 115 V output with a Fluke 27 in min/max mode at power disconnect, i.e., powering down with the off pushbutton. Less than a volt variation and that is well within the short normal line voltage variation. Thus, upon a sample of one I did not see a likely switching transient problem.
There is nothing so far that seems to make sense relative to the cause of your failures.
Do these machines have any external equipment connected to them? Computers, robots, etc?
.