Is it bonded at the first means of disconnect, wherever it may be? There seems to be a lot of confusion on this.
Stating the system has a neutral, we have to assume it is a grounded system. On the POCO side of the service disconnecting means (SDM), all exposed, non-conducting metallic parts are bonded to the neutral [grounded conductor].
This system is required to have the Main Bonding Jumper (MBJ) installed in the SDM enclosure, between the neutral and equipment grounding system (EGS).
On the consumer side of the SDM, no neutral is to be bonded to the EGS (except separately derived systems that have a grounded neutral conductor).
Keep in mind that some POCO's, for some systems, may require a disconnect (typically non-fused) on the supply side of the meter or CT cabinet for maintenance purposes. This is not the SDM.