JDB3
Senior Member
- Location
- San Antonio, Texas
Having a discussion, what is the permissible capacity of 1/0 SER Al. feeding a sub-panel when passing through insulation in a residence? :?
By the 2014 code, is there still something about if the wire is on a 100 amp or larger breaker/over current device and terminates on device listed for 75 or 90 degrees, then you may use the 75 degree column? :?
Having a discussion, what is the permissible capacity of 1/0 SER Al. feeding a sub-panel when passing through insulation in a residence? :?
338.10(A)(4) Installation Methods for Branch Circuits and Feeders.
(a) Interior Installations. In addition to the provisions
of this article, Type SE service-entrance cable used for interior
wiring shall comply with the installation requirements
of Part II of Article 334, excluding 334.80.
Where installed in thermal insulation, the ampacity shall
be in accordance with the 60?C (140?F) conductor temperature
rating. The maximum conductor temperature rating
shall be permitted to be used for ampacity adjustment and
correction purposes, if the final derated ampacity does not
exceed that for a 60?C (140?F) rated conductor.
:huh: Are you saying that 110.14 (c) (1) (b) (1) does not apply? Sorry,,I do not understand why it would not? :?
:huh: Are you saying that 110.14 (c) (1) (b) (1) does not apply? Sorry,,I do not understand why it would not? :?
Having a discussion, what is the permissible capacity of 1/0 SER Al. feeding a sub-panel when passing through insulation in a residence? :?
. The one HUGE difference is that in 334.80, the allowance in 310.15(A)(2) does not apply....this is not the case in 338.10(B)(4)(a) as a whole. Which for those working with SE Cable can be HUGE.
Anyway...those are my opinions and i'm sticking with it (unless someone makes me change it..lol...:angel
Only one problem, 310.15(A)(2) ain't gonna work for SER in thermal insulation. You only have one final ampacity. No portion is higher or lessor. The 60C does not just apply to the portion in the insulation.
Well, just because I am wrong, that does not mean I gotta agree...
Aw, phooey................
Well now...that's a bit of a loaded question to answer now isn't it.
1) Are you using 310.15(B)(7) allowances (correctly)
2) Have you applied 338.10(B)(4)(a) properly...and if so will 310.15(A)(2) help your situation. In other words, how much thermal insulation are you speaking about.
While I was at the IAEI Western Section event their seemed to be quite a bit of confusion regarding Section 338.10(B)(4)(a) and being installed in insulation. I got with a few of the individuals and explained that while 338.10(B)(4)(a) exempts the demands of 334.80, the reason it does so is because 338.10(B)(4) has it's own thermal insulation requirements that must be followed. The one HUGE difference is that in 334.80, the allowance in 310.15(A)(2) does not apply....this is not the case in 338.10(B)(4)(a) as a whole. Which for those working with SE Cable can be HUGE.
Anyway...those are my opinions and i'm sticking with it (unless someone makes me change it..lol...:angel
When used as a feeder or branch circuit, all rules for NM-B cable apply. There is no allowance for using 310.15(A)(2).
Dave Mercier Southwire Company
I brought that up in another thread and I wrote an email to Dave Mercier. He does not agree with you. I mention how art. 338 does not excluded the 310.15(A)(2) and he never responded.
Here is his response-- I think he is incorrect- may be the intent but it is not what the code states
Is Dave Mercier a CMP member or IAEI or just works at Southwire? Just curious.
CMP and it was he who got the seu dropped to 60C.
LOL... I also edited my post and added a bit of commentaryWell, if he is is a CMP member and agrees with me, then he's gotta be correct......:angel: