I recently installed a 1kW array on my home, and had the rough-in inspection today. It is a microinverter based system, using listed grounding washers as equipment grounding conductors for connections between modules, racking, and microinverters. From the microinverters, #12 (20A breaker) conductors run through the attic in romex, and down the exterior of the house to the AC disconnect in conduit.
The AHJ has requested that the EGC be minimum #6, all the way from the inverter to the grounding electrode, based on 690.46. I'm not getting my hopes up, but I intend to try to argue this with the inspector, as he was not familiar with the requirements and had to look them up on-site during the inspection. 690.46 references 250.120(c), which I think makes it fairly clear that the EGC size is appropriate, and I think I can argue this point. However, he also wants the EGC to be connected directly to the ground rod and will not accept the connection to the main switchboard ground bus as it stands now. I have no idea where he's getting this, anyone run into this requirement before?
Unfortunately this caught me off guard and I did a fairly poor job of arguing this at the time of the inspection.
The AHJ has requested that the EGC be minimum #6, all the way from the inverter to the grounding electrode, based on 690.46. I'm not getting my hopes up, but I intend to try to argue this with the inspector, as he was not familiar with the requirements and had to look them up on-site during the inspection. 690.46 references 250.120(c), which I think makes it fairly clear that the EGC size is appropriate, and I think I can argue this point. However, he also wants the EGC to be connected directly to the ground rod and will not accept the connection to the main switchboard ground bus as it stands now. I have no idea where he's getting this, anyone run into this requirement before?
Unfortunately this caught me off guard and I did a fairly poor job of arguing this at the time of the inspection.