(A) Types CL2P and CL3P. Types CL2P and CL3P plenum
cable shall be listed as being suitable for use in ducts,
plenums, and other space for environmental air and shall
also be listed as having adequate fire-resistant and lowsmoke
producing characteristics.
Informational Note: One method of defining a cable that is
low-smoke producing cable and fire-resistant cable is that
the cable exhibits a maximum peak optical density of 0.50
or less, an average optical density of 0.15 or less, and a
maximum flame spread distance of 1.52 m (5 ft) or less
when tested in accordance with NFPA 262-2011, Standard
Method of Test for Flame Travel and Smoke of Wires and
Cables for Use in Air-Handling Spaces.