I have a question about the New Jersey rehab subcode. The last thread was ruined by somebody who wanted to tell me what he would do (and wouldn't give up on that) instead of what code requires me to do. I don't think it's fair that my question goes unanswered, so I started a new thread and hopefully we can stay on the topic and discuss code requirements only. This is a code forum, and knowing the code is never a bad thing, even if it's more lenient than you personally like.
Again, the disclaimer: My question is about the NJ rehab subcode. I know many people will say "Upgrade the grounding, it's the right thing to do!" but I would like to know the actual code requirements based on the NJ Rehab Subcode, since that is all the customer is willing to pay for (and rightly so).
I have a customer who is selling his house. The buyers want him to replace a 200A FPE disconnect on the outside of the house because it's an FPE (it's also rusted and in bad shape), he agreed to have that done.
My concern is the way it's setup. The disconnect is fed from the meter base above it with 3 wires. Then a 4-wire SER cable runs from the disconnect into the house to a MLO panel in the basement. All that is fine.
The issue is that the only grounding is a conductor from the water pipe to the ground bar inside of that MLO panel. The outside disconnect has no GEC running to it, only the EGC inside of the SER cable.
The NJ rehab subcode allows us to install a new panel or disconnect without having to upgrade the grounding, which I do often and it always passes. The problem here is that there is no GEC at all, so this is new territory for me.
I told the customer that the inspector might give us a problem, but he doesn't want to pay for the grounding if code doesn't require it, especially since his basement is finished and running the GEC will not be easy.
Has anyone in NJ come across a situation like this or know the rehab subcode well?
Again, the disclaimer: My question is about the NJ rehab subcode. I know many people will say "Upgrade the grounding, it's the right thing to do!" but I would like to know the actual code requirements based on the NJ Rehab Subcode, since that is all the customer is willing to pay for (and rightly so).
I have a customer who is selling his house. The buyers want him to replace a 200A FPE disconnect on the outside of the house because it's an FPE (it's also rusted and in bad shape), he agreed to have that done.
My concern is the way it's setup. The disconnect is fed from the meter base above it with 3 wires. Then a 4-wire SER cable runs from the disconnect into the house to a MLO panel in the basement. All that is fine.
The issue is that the only grounding is a conductor from the water pipe to the ground bar inside of that MLO panel. The outside disconnect has no GEC running to it, only the EGC inside of the SER cable.
The NJ rehab subcode allows us to install a new panel or disconnect without having to upgrade the grounding, which I do often and it always passes. The problem here is that there is no GEC at all, so this is new territory for me.
I told the customer that the inspector might give us a problem, but he doesn't want to pay for the grounding if code doesn't require it, especially since his basement is finished and running the GEC will not be easy.
Has anyone in NJ come across a situation like this or know the rehab subcode well?