I gotta run an 120v outlet out 400' on a bridge. The volt drop calc says i need a #4 to #2. Can I buck the voltage up at the beginning and use a smaller wire?
I gotta run an 120v outlet out 400' on a bridge. The volt drop calc says i need a #4 to #2.
Can I buck the voltage up at the beginning and use a smaller wire?
That sounds excessive.
What did you use as the load current for the voltage drop calculator?
No, the problem with that idea is the 'no load' voltage will be too high at the far end.
You could send 240 out to the bridge which would cut the current in half and reduce the wire size. At the far end you would install a 240 to 120 transformer.
I agree that a step down might be a better solution maybe even 480/120 if available.
I'm wondering, for a bridge what would you use as the grounding electrode for the derived neutral?
It's on the beach.
I did 20amp for the load.