Member
- Location
- Tacoma, WA
The situation: Parallel 480VAC 3 phase MC feeders, using 3/c w/gnd cable, industrial facility, not previously required by a state inspector to oversize the EGC to meet NEC 2008 250-122(F).
Art. 250-118(10) allows the use of the corrugated tube-type armor as an EGC. The cable manufacturer UL's the armor for use as an EGC but does not give it's equivalent AWG size. Can we assume that the armor equals the copper ground conductor AWG that is provided in the MC Cable and therefore use the total of the two to satisfy Art. 250-122(F)? Is there an exception by interpretation from AHJ's that allows installations to utilize the armor and installed ground conductor without having to provide a 4/c w/gnd MC cable to meet 250-122(F)?
Art. 250-118(10) allows the use of the corrugated tube-type armor as an EGC. The cable manufacturer UL's the armor for use as an EGC but does not give it's equivalent AWG size. Can we assume that the armor equals the copper ground conductor AWG that is provided in the MC Cable and therefore use the total of the two to satisfy Art. 250-122(F)? Is there an exception by interpretation from AHJ's that allows installations to utilize the armor and installed ground conductor without having to provide a 4/c w/gnd MC cable to meet 250-122(F)?