Practice test questions
What is the demand lighting load in a 2,200 square foot home?
For the demand load you add the two 1,500 watt small appliance circuits and one 1,500 watt laundry then apply demand factor, so, 6,600+ 4,500= 11,100-3000 x .35 + 3,000 = 5,835VA
What is the general lighting load for a 3,200 square foot home? In this question you do not apply the two 1,500 watt small appliance circuits and one 1,500 watt laundry? So, 9,600VA
Any info is appreciated, I dont have the answer key. Thanks