Roof Top Unit - under Zone of Protection

Status
Not open for further replies.

Ranger86

Member
Location
Las Vegas, NV
NFPA 780 (2011 edition), section 4.8.10.3 reads, " at least 2 main-size conductors shall be installed to connect the unit to the lightning protection system ". If the RTU is under a zone of protection, does this section still apply ?
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
NFPA 780 (2011 edition), section 4.8.10.3 reads, " at least 2 main-size conductors shall be installed to connect the unit to the lightning protection system ". If the RTU is under a zone of protection, does this section still apply ?

See the text of 4.8.10.
 

Ranger86

Member
Location
Las Vegas, NV
4.8.10 talks about strike termination devices. It is not clear to me if section 4.8.10.3 applied only if it is not located in a zone of protection. So basically, what you are referring to (I assume) is that if it is under a zone of protection, then none of 4.8.10.1 thru 4.8.10.3.2 apply. Is this correct ?
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
4.8.10 talks about strike termination devices. It is not clear to me if section 4.8.10.3 applied only if it is not located in a zone of protection. So basically, what you are referring to (I assume) is that if it is under a zone of protection, then none of 4.8.10.1 thru 4.8.10.3.2 apply. Is this correct ?

Yes. 4.8.10 says that strike termination devices shall be required...on all rooftop mechanical units with continuous metal housings less than 3/16" thick...that are not located in a zone of protection.
 