let see if I can explain this, and I know I have to talk to the local AHJ,but would like to know you all opinion first:
We are designing a health facility, which will included and standby emergency generator, and as you know there is 10 second waiting period (most of the time less than 10 sec) for the generator to kick and take over. Because of that lapse in time, the electrical inspector required that emergency light fixtures has their own battery pack to ensure a continuous path of egress at all time (which means no 10 sec or less is accepted).
here is my questions we are proposing a central UPS, for the computers system, but such UPS does not satisfy NEC 700.12 requirements of 1.5 hours, it does provided instantaneous power for a limited 12-15 min, way under the required 1.5 hr.
can the combination of the instantaneous UPS and the Standby generator satisfy the NEC requirements?
the intention is to save the client the expensive battery pack for LED fixtures, is five flour building, and the cost can add up quickly.
Thanks
We are designing a health facility, which will included and standby emergency generator, and as you know there is 10 second waiting period (most of the time less than 10 sec) for the generator to kick and take over. Because of that lapse in time, the electrical inspector required that emergency light fixtures has their own battery pack to ensure a continuous path of egress at all time (which means no 10 sec or less is accepted).
here is my questions we are proposing a central UPS, for the computers system, but such UPS does not satisfy NEC 700.12 requirements of 1.5 hours, it does provided instantaneous power for a limited 12-15 min, way under the required 1.5 hr.
can the combination of the instantaneous UPS and the Standby generator satisfy the NEC requirements?
the intention is to save the client the expensive battery pack for LED fixtures, is five flour building, and the cost can add up quickly.
Thanks