CLEARANCES FOR SIGNS FROM OVERHEAD ELECTRICAL TRANSMISSION LINES.

Status
Not open for further replies.

mgookin

Senior Member
Location
Fort Myers, FL
The local electric utility will have standards for that and they are often very willing to provide all the assistance you need for design & construction to make sure everyone's safe.

To tell you what they require here could possibly mislead you.

When you inquire you need to contact their construction division.
 

jumper

Senior Member
If the voltage is above 1000V the NEC has this:

Informational Note: For clearances of conductors of over
1000 volts, nominal, see ANSI C2-2007, National Electrical
Safety Code.

I believe POCOs use NESC.
 

kwired

Electron manager
Location
NE Nebraska
If the voltage is above 1000V the NEC has this:

Informational Note: For clearances of conductors of over
1000 volts, nominal, see ANSI C2-2007, National Electrical
Safety Code.

I believe POCOs use NESC.

If NEC applies, there is likely some AHJ that can force a change if out of compliance with NEC.

If it is POCO owned, they are not necessarily forced to use NESC, but many do as a CYA tool.

If the sign was there first they will modify their line construction or even make compromises with sign owner to try to comply with NESC and make everyone involved happy.

If the line was there first - they probably have a right of way or easement and they get priority over what happens in that area.
 