I am on a project where we are installing appx. 10 30kva-65kva transformers fed from one distribution panel. All transformers GEC will be tied into a single Grounding Bar that goes to building steel. Am I correct in saying the GEC sizing to the ground at should be the sum of all 10 GEC's to the transformers?


Sent from my iPhone using Tapatalk
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I agree with Bob #3/0 is the minimum and the maximum required for a common grounding electrode that serves more than one transformer.
 

bcnj

Member
Location
NYC
So even if I had 100 30kva transformers it will still be a 3/0?

I am thinking it 250.66 Note#1 is applicable.

Notes:
1. Where multiple sets of service-entrance conductors are used as permitted in 230.40, Exception No. 2, the equivalent size of the largest service-entrance conductor shall be determined by the largest sum of the areas of the corresponding conductors of each set.


Sent from my iPhone using Tapatalk
 

jumper

Senior Member
So even if I had 100 30kva transformers it will still be a 3/0?

I am thinking it 250.66 Note#1 is applicable.

Notes:
1. Where multiple sets of service-entrance conductors are used as permitted in 230.40, Exception No. 2, the equivalent size of the largest service-entrance conductor shall be determined by the largest sum of the areas of the corresponding conductors of each set.


Sent from my iPhone using Tapatalk

You would still end up with a 3/0
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
So even if I had 100 30kva transformers it will still be a 3/0?

I am thinking it 250.66 Note#1 is applicable.

Notes:
1. Where multiple sets of service-entrance conductors are used as permitted in 230.40, Exception No. 2, the equivalent size of the largest service-entrance conductor shall be determined by the largest sum of the areas of the corresponding conductors of each set.


Sent from my iPhone using Tapatalk

Not applicable:

Is these transformers are fed from a distribution panel the secondaries would not be service conductors.
Note 1 applies to parallel condcutors (connected together at both ends)
 

bcnj

Member
Location
NYC
You are getting the size of the EGC based off of table 250.66. The table is labeled for service conductors.

Also, in theory, can someone argue that there is or is no limit to the amount you can place in a 3/0 wire?


Sent from my iPhone using Tapatalk
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
You are getting the size of the EGC based off of table 250.66. The table is labeled for service conductors.

Also, in theory, can someone argue that there is or is no limit to the amount you can place in a 3/0 wire?


Sent from my iPhone using Tapatalk
ECGs are never sized using Table 250.66.
 

bcnj

Member
Location
NYC
Except 250.66 Note 1

Notes:
1. Where multiple sets of service-entrance conductors are used as permitted in 230.40, Exception No. 2, the equivalent size of the largest service-entrance conductor shall be determined by the largest sum of the areas of the corresponding conductors of each set.



Sent from my iPhone using Tapatalk
 

bcnj

Member
Location
NYC
Add the Circular Mils for each GEC and make sure your main GEC is equal or greater.


Sent from my iPhone using Tapatalk
 

Smart $

Esteemed Member
Location
Ohio
Except 250.66 Note 1

Notes:
1. Where multiple sets of service-entrance conductors are used as permitted in 230.40, Exception No. 2, the equivalent size of the largest service-entrance conductor shall be determined by the largest sum of the areas of the corresponding conductors of each set.
You cannot exceed "Over 1100" or "Over 1750". :huh:
 