Abraham2015
Member
- Location
- Los Angeles, CA
We are having problems with an electrical panel. It's a single phase 120 volt panel. Two hot legs and one neutral coming into the panel. There are about 8 circuit breakers connected to the panel. We removed all of the wires from the circuit breakers and tested resistance of each circuit breaker in the on and off position. No issues detected. We then tested voltage across each circuit breaker and between phases. No issues. However, when we connected one circuit breaker, there was a voltage drop down to 90 volts. There is a similar problem with other circuits but not as severe. Some circuits suffer from over voltage of about 140 volts. Could this problem be caused by several loose connections or neutral wires? Any other ideas?