Generator Grounding as a separately derived system

Status
Not open for further replies.
For a generator that is grounded as a separately derived system, is it common to bring the ground electrode conductor back to the building ground electrode system or create a new ground electrode system (ground rods in generator area)? If a new ground electrode system is provided is it required to bond to the building ground electrode system?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
From what I understand unless the manufacturer requires ground rods or some other electrode at the generator itself then it is not required.
 
So since its a separately derived system that requires a ground electrode connection, you would suggest bringing a ground electrode conductor directly to the building ground electrode system?
 
I guess to answer my own question, 250.30 (A) (7) would require the ground electrode to be as near as practical, which in my opinion would mean driving ground rods in a outdoor generator application. I guess my only other question is do I need to bond this electrode to building ground electrode system
 

Smart $

Esteemed Member
Location
Ohio
Assuming the generator has an integral disconnecting means with OCPD, the bonding will be handled by the EGC run with the feeder.
 