I would like to run this by someone other than me. I am going to add a sub-panel and I?m not sure if my calculations are correct.
Room addition with kitchen remodel:
Room addition 540sqft x 3= 1,620
Kitchen SA 2 x 1500= 3,000
Refrigerator 1500= 1,500
Microwave 1500= 1,500
Island SA 1500= 1,500
Can Lt. in Rm add. 8 x 60w= 480
Freezer 1,500
Total 11,100 3,000
8,100 x 35% 2,835
Total 5,835
Double Oven 7.2KW= 7,200 x 100% 7,200
Total 13,035
13,035 / 240
Total 54.3125
Breaker amp for Sub panel 60 amps
Any input of this will be greatly appreciated.