Lightninarrester
Member
Your Input appreciated, I am working on a 1200KW, 13.8kv, 3P, 4Wire Emergency Generator (Neutral Grounded through resistance). The generator cables from the generator go through a disconnect then to a 15kv breaker then to a step down transformer 1500kva 13.8/480Y-277V, then to another 480 breaker. Q1) Do I carry the neutral from the generator and the ground with the phase cables or just three phase cables and the grounded neutral. Q2) Do I bond the generator neutral to the first 15kV breaker enclosure. Q3) Do I keep carrying the neutral (Ground) all the way to the 480V breaker enclosure. Q4) At the low side of the transformer do I carry in each conduit a neutral.