K-Rated Transformer

Status
Not open for further replies.

danilo

Member
Guys,

supposed in my computation for getting the k factor of transformer i got k=4. what would be its possible effect in the system if i use k=13 rated transformer instead?

Gracias!

Danilo
 

charlie

Senior Member
Location
Indianapolis
Re: K-Rated Transformer

It will work fine. You will get more core steel, a larger grounded conductor, and a higher cost but the transformer will work just fine. :D
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
Re: K-Rated Transformer

The K-Rating is a measure of the transformer's ability to tolerate the heat generated by the harmonic currents. You would simply be using a transformer that can tolerate more abuse that it is likely to see. It would be a bit of overkill, with a corresponding overcost, as Charlie said. But it gains you nothing in terms of extra capacity for adding load, and the distribution system will not notice the difference.

Danada.
 

ron

Senior Member
Re: K-Rated Transformer

Three downsides of using a larger K rating than needed are that:
some manufacturers design the xfmr with a reduced impedance (from standard)
have higher inrush (since they sometimes use a somewhat standard large transformer and derate it) than you might expect for the nameplate size
and are physically larger than a typical xfmr or smaller k rating.
 