hotel room calcs

Status
Not open for further replies.

bwyllie

Senior Member
Location
MA
When doing a load calc on a hotel, do I add 2va/sf + 1500VA for a bathroom circuit and apply the approriate demand as per 220.42 and then add any HVAC units load?

Thank you.
 

bphgravity

Senior Member
Location
Florida
Re: hotel room calcs

Looks good to me. Don't forget the hall lighting or any other common area lighting are continuous loads and have different va/ft? allowances.
 