Originally posted by wannabe:
Is there a rule of thumb for selecting a neutral wire size, it was mentioned that it was doubled?
Not that I have seen, many jobs we do are engineered with super neutrals.
For panel feeders the most common super neutral I see is simply running double neutrals.
For example a feeder to a 3 phase 225 amp panel might be engineered with five 4/0 CU THHN, one for each ungrounded and two for the neutral.
Please note that this super neutral is basically useless unless the panel is ordered with a larger neutral bus.
Typically what I will see is a 225 amp panel with a 400 amp rated neutral bus. Also this panel should be fed by a transformer that is either over sized or "K" rated.
Now as Ron mentioned super neutrals can also be used on branch circuits, for a 20 amp multiwire branch circuit it is very common to use 12 AWG for the ungrounded and 10 AWG for the neutral.
All of this is design choice and not NEC requirements.
I just recently ran two 3 phase feeders to a small computer room.
Here is what the engineer chose for the job.
80 amp feeder overcurrent protection.
Three 1 AWG CU THHN ungrounded conductors. (Rated 150 amps)
One 2/0 CU THHN Neutral conductor. (Rated 195 amps)
100 amp Main lug panel with standard 100 amp neutral buss.
In my opinion we should have been directed to install a 200 amp Neutral buss if the 2/0 Neutral is expected to be loaded.
IMO Super Neutrals are of questionable value.
I say this because it is unusual to find the circuits in question loaded anywhere near their rating.
A 20 amp circuit feeding non-linear loads is often only loaded up to about 4 or 5 amps.