Odd Feeder Size

Status
Not open for further replies.

muhandas

Senior Member
In looking at a set of plans for a a group of townhouses I find 280 MCM (I know it should be kcmil, but that is what the plans have) aluminum feeders for 200A service. That size struck me as odd, frankly I had never run across that before. I don't even know if there are conductors manufactured in that size. Could that just be a typo?
Any comments would be appreciated.
Heinz R.
 

steve66

Senior Member
Location
Illinois
Occupation
Engineer
250kcm is normally 255 amps.

3/0 is usually good for 200A.

You might bid it as 300KCM (the next size up from what the print says) just to cover any upsizing the engineer might be doing for voltage drop.

Steve
 