Would a 600w 230v 1 phase gate motor work properly with a 208 volts????

This is very puzzling for me. I had another "electrician" tell me it would because of the 10% rule.

:confused:
 

al hildenbrand

Senior Member
Location
Minnesota
Occupation
Electrical Contractor, Electrical Consultant, Electrical Engineer
Re: Gate Motor

The single best source of authority will be the gate manufacturer's customer service department. Call them with the model number and ask.
 

jimwalker

Senior Member
Location
TAMPA FLORIDA
Re: Gate Motor

If a motor was intended to run on 208 or 230 it would be labeled 208/230.
So if the 230 was 10% low that would be 207
Your supplying 208 if that was 10% low we have 187
now we have a motor wanting 230 and getting 187
not too kool
 

tom baker

First Chief Moderator
Staff member
Re: Gate Motor

A motor designed for 208 v will be labled 200V. Motor have a lower name plate rating than the system voltage to allow for voltage drop.
Using a 230 V motor where a 200 V motor is required would result in low votage to the motor,and is a violation of 110.3(B)
 

jimwalker

Senior Member
Location
TAMPA FLORIDA
Re: Gate Motor

Often i see AC units that are stamped 208/230.
That indicates the motor is fine on either along with 10% allowed by poco.If the motor is stamped 230 then it is not designed for 208.Doing so might just land you a bill for a new motor.
Chances are it will work on 208but can you afford that chance?

[ December 21, 2003, 02:45 PM: Message edited by: jimwalker ]
 

djtazjr

Member
Re: Gate Motor

Thanks Guys, especially for the code article. Now I have some backup for me. This guys thinks he knows everything about the code and he ins up wrong 80% of the time.

:)
 