okay guys, here's my question. i have a 20A ckt, load is just lighting but the problem is the when i compute for the voltage drop, it calls for me to put in a #6 cable. How do you install a #6 cable to a 20A CB?
Thanks a lot.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: cables and CB's

Just splice a piece of #12 on the #6.
You could actually run a #12 to a jbox a short distance from the panel and change to #6 at that location. The circuit could start and end with smaller wire as long as the total resistance compensates for the VD.

Roger
 

jimwalker

Senior Member
Location
TAMPA FLORIDA
Re: cables and CB's

Keep in mind the code doesn't say anything about voltage drops.They are only foot notes that suggest a limit.Nothing wrong in splicing #6 to # 12 in the panel.Just how bad would the voltage drop be in #12 or #10 a drop to 110 wouldn't bother me on lights only.Actually it be easier on the bulbs.
 