Voltage drop??

Status
Not open for further replies.
I'm looking for any and all suggestions as to how best(i.e. most cost effective/efficient)to get 60 amps 240 volts single phase 1200 feet thanks i look forward to hearing from you all
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: Voltage drop??

Is the load really 60 amps or just the panel size?

How much voltage drop are you willing to live with?

60 amp load, 240 volt 3% drop 1200 feet.

I come up with one 300 kcmil copper per phase.

Transform it to 480 volt and I come up with one 2 AWG copper per phase.
 

bob

Senior Member
Location
Alabama
Re: Voltage drop??

Using the higher voltage is the answer just as Bob said. I would be interested in the cost of 2 transformers and 1200 ft of 3# 2cu as opposed to 1200 ft of 2#300 cu + #? neutral.
 
Re: Voltage drop??

The load is really 60 amps and 5% voltage drop is tolerable if we boost the voltage we will have to step it back down i am i correct ? because my calculations show a voltage loss of around 71 volts ?
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
Re: Voltage drop??

We did this last year with two transformers. We wanted the smallest current (for lowest voltage drop) so we used one transformer to go from 240-600V and a second transformer to go from 600-120/240. For 60A at 240V single phase you would need 15KVA units.
 