splinetto said:1. What does the B stand for? I was told it was for 90 degree conductors and if so do I still have to use the 60 degree column?
2.Never thought of this before but can you #8 NM (60 degree) to a jbox and splice on #10 THHN and be compliant?
What does the B stand for? I was told it was for 90 degree conductors and if so do I still have to use the 60 degree column?
Never thought of this before but can you #8 NM (60 degree) to a jbox and splice on #10 THHN and be compliant?
But it would be ok if the terminals were rated at 90 degree?raider1 said:Since the terminals that you connect the #10 THHN to are more than likely not rated at 90 degrees you would not be able to use the 90 degree rating of the #10 THHN for the conductor ampacity.
Chris
splinetto said:1. What does the B stand for? I was told it was for 90 degree conductors and if so do I still have to use the 60 degree column?
2.Never thought of this before but can you #8 NM (60 degree) to a jbox and splice on #10 THHN and be compliant?
No-- and I doubt you would find 90 C terminalssplinetto said:But it would be ok if the terminals were rated at 90 degree?
Dennis Alwon said:No-- and I doubt you would find 90 C terminals
iwire said:On equipment I agree 100% :smile:
For splicing there are a number of options rated at least 90C.
Dennis Alwon said:Yeah but somewhere you will be connected to a 75C terminal.
splinetto said:What about this scenario 4/3 romex(70a) to #6 THHN (65a)?
iwire said:I think what he was suggesting was using smaller conductors in the middle of a run. Lets say 6 AWG at breaker, change to 8 AWG for the run and then back to 6 AWG at the equipment.
That would be legal, the biggest problem is once the run gets long enough to make doing this worth while the run is also long enough that voltage drop will become a problem.
Dennis Alwon said:The op says #10- so I don't believe you can do that since 240.4(D) plays a hand here.
jwelectric said:Well lets say that using the 90 degree column to derate and the math came to 12 amps. Could a 15 amp overcurrent device then be used on a #14 conductor using 240.4(B)?