Got a call today from POCO...They were energizing 4 services on a building for me. (It's legal not the point). The foreman calls and says there is current on the 400Amp service. I tell him it's because the CTs and Meter are causing it. I almost had to go to work and educate the POCO crew today. I found out after 50 questions one of the crew checked continuity between phases and to ground. No current is present. What the guy was reading was the continuity through the 3ph meter.
The setup is a transocket with CTs for each phase and then voltage taps. Seven wires run out to a KWH meter.
This is the 3rd time I've gotten calls like this from the POCO. Maybe they'll figure it out...nah!
Think I'll call on Monday...