bcsmith

Member
I am looking to get information on the code requirerments for installing an 112.5 KVA transformer. The transformer was installed in 1996, thus I need to obtain code info from 1996. I believe the original installation was sized improperly.:mad:
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
I am looking to get information on the code requirerments for installing an 112.5 KVA transformer. The transformer was installed in 1996, thus I need to obtain code info from 1996. I believe the original installation was sized improperly.:mad:
Article 450 has had very few changes to it. I believe table 450.3 is still the same.

What specific questions do you have?
 

bcsmith

Member
Nec 1996

112.5 KVA
4.5 % IZ
HV-480, HA-135
Lv-240, LA-271
Class AA
150 C

If the code hasn't changed much and my math is correct:

Primary OC protection should be 168.75 or 175 breaker size
 

cadpoint

Senior Member
Location
Durham, NC
Wasn't it in the 90's that the NEC let an odd situation out for a cycle.

Wasn't that in respects to 310.16 or another table were wire rating and derating was oddly changed ? I'm sorry again od to the memory!
 

iwire

Moderator
Staff member
Location
Massachusetts
112.5 KVA
4.5 % IZ
HV-480, HA-135
Lv-240, LA-271
Class AA
150 C

If the code hasn't changed much and my math is correct:

Primary OC protection should be 168.75 or 175 breaker size

Assuming the unit has secondary protection (it should) I come up with an NEC maximum primary overcurrent protection value of 338 amps or a 350 breaker size.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
112.5 KVA
4.5 % IZ
HV-480, HA-135
Lv-240, LA-271
Class AA
150 C

If the code hasn't changed much and my math is correct:

Primary OC protection should be 168.75 or 175 breaker size

Almost, but not quite.

The NEC does not specify a OCPD specific size. Basically for 600V, it says the primary OCPD must not exceed 125% of the primary amps unless you have secondary protection. If you have secondary protection of not more than 125% secondary amps, you are allowed, but not required, to have your primary OCPD larger than 125%.
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
Assuming the unit has secondary protection (it should) I come up with an NEC maximum primary overcurrent protection value of 338 amps or a 350 breaker size.
I have 350 for the secondary OCPD, and I agree with 175 for primary. But is this a 240 delta secondary, or is it one of those wierd high leg thingys that I have never (fortunately) had to deal with? :-? :wink:
 

M. D.

Senior Member
Is this the correct math?
PRI
122,500va / (480x1.732)= 135a

135a x 1.25= 169
next higer standard = 175a




SEC
112,500va / (240x1.732) = 270a

270a x 1.25= 337.5A

next standard 350amp
 

iwire

Moderator
Staff member
Location
Massachusetts
I have to try again. :smile:

Is this the correct math?
PRI
122,500va / (480x1.732)= 135a

135a x 1.25= 169
next higher standard = 175a

I get this

PRI
122,500va / (480x1.732)= 135a

135a x 2.5 = 337 amps
next higher standard = 350a



SEC
112,500va / (240x1.732) = 270a

270a x 1.25= 337.5A

next standard 350amp

I get the same for the secondary.
 
Last edited:

e57

Senior Member
I have to try again. :smile:



I get this

PRI
122,500va / (480x1.732)= 135a

135a x 2.5 = 337 amps
next higher standard = 350a





I get the same for the secondary.
Bob wheres the 2.5 come from???? Or is it one of those reversed math tricks - like 80% of 125% is the same....
Y*1.25=Z
Z*.8=Y
 

Goroon

Member
?..Primary OC protection should be 168.75 or 175 breaker size..?

?..Primary OC protection should be 168.75 or 175 breaker size..?

With Primary and Secondary protection FOR THE Transformer as the Equipment.
Primary protection has no Note 1 for Primary, ie.. ?next higher standard?
Secondary protection does. [240.6 Standard Ampere Ratings.]

Would not Primary OCP be stated at be 150 for the 168.75 or 300 for the 338 calculations.?

(112KVA x 1000)/831,3ph = 135.3 Amp transformer Primary, 169.1 @125% or 338.3 @ 250% if secondary provided.

At this point I Select Wire per 240.4 Protection of Conductors. #1, 75C @ 150A to 300kcmil for the 300A

Is this not correct?
 

iwire

Moderator
Staff member
Location
Massachusetts
Is this not correct?

In my opinion there is no correct answer, a lot of it is design decisions.

Your answer will work but it is not the maximum the NEC allows.

In this case the NEC will allow a 350 amp breaker on both the primary and secondary size.
 