bath room circuits in a resi dwelling

Status
Not open for further replies.

bob sztuk

Member
the code states 1 -20 amp circuit as a bathroom circuit. can you use 1 circuit for 2 bathrooms in a apartment or condo? The exception states multiple outlets in 1 bathroom off 1 circuit. Does the code allow you to feed bathroom 2 from bathroom 1?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Re: bath room circuits in a resi dwelling

You can only feed the receptacles from one bathroom to the other. Nothing else.
 

jimwalker

Senior Member
Location
TAMPA FLORIDA
Re: bath room circuits in a resi dwelling

You can pick one of two ways.All bathroom receptacles on 1 20 amp circuit with no lights or other outlets.Or a dedicated 20 amp circuit for each bathroom and they then could include everything in just that 1 bathroom.
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
Re: bath room circuits in a resi dwelling

The rule does apply to apartments and to condos. Both count as "dwelling units."

[ December 29, 2005, 05:55 PM: Message edited by: charlie b ]
 