Generator block heater receptacle

Status
Not open for further replies.

tshea

Senior Member
Location
Wisconsin
Checked the code book but couldn't find anything requiring the generator block heater receptacle to be GFI protected. Anyone find something different? We used a single receptacle (simplex) with bubble cover. Receptacle is located inside generator housing enclosure.

[ February 04, 2004, 09:32 PM: Message edited by: tshea ]
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: Generator block heater receptacle

It does not need to GFI protected and shouldn't be.

You could hard wire this with a single pole switch inside the generator housing for a disconect if you wanted to, (prefered in my opinion) a plug connection close to a vibrating generator is not the best scenario.

Roger
 