Status
Not open for further replies.

DPW

Member
Location
FT. SMITH, AR
It my understanding that this revised section will require power distribution blocks to be installed with a cover.

Does this mean that terminal blocks (120vac) mounted in a standard 4X4 box would be an exception or does the enclosure have to be over 100cu in?

If an additional component such as a fuseblock was mounted in the jbox, would it require an insulated cover as well?
 

raider1

Senior Member
Staff member
Location
Logan, Utah
That section applies to distribution blocks installed in boxes larger than 100 cubic inches.

A 4x4 cbox is not larger than 100 Cubic inches so it does not apply to them.

Chris
 