bassphisher
Member
I am inspecting a hallway that was installed between two buildings in an assisted living center.This is not your normal hallway.It is more like an awing with sides.Tent like with 2x2 metal frame bolted to the sidewalk.The sides of this tent-hallway does not touch the sidewalk so when it rains the wind can blow water underneath.Its all piped in with emt and set screw fittings,4 square boxs.They want to install 8-3000watt/208v radiant heaters.These will be fed from a the only panel in this building.It has a 175Amp main breaker.I am going to ask them to do a service calculation since they are attempting to add 100Amps of continuous load to this panel.I suspect that they do not have enough ampicity for this additional load.They want to feed these heaters with 2-60Amp breakers #6 wire.Violation of 424.3(A).They want to tap these #6s with #12s to feed a dual fused switch(sty)that will feed an individual receptacle that they will plug the heaters into.Seems like their are a lot of violations here.Also no lights are installed.Its supposed to be day use only,for physical therapy.Your help is appreciated.