Pull box sizing

Status
Not open for further replies.
When sizing j-boxes/pull boxes, according to art. 314.28 (A), if you don't have any #4 or larger in the system, is it necessary to multiply the largest conduit by 6 (or 8, depending on angle or straight pulls)? It's unclear to me if an 8x8 box with 1 1/4" conduits entering the left and right sides is allowed, if all conductors are smaller than #4.
 

kiloamp7

Senior Member
Re: Pull box sizing

If all conductors involved are smaller than #4, don't you go by the cubic inch per conductor method ?
 