fire stopping

Status
Not open for further replies.

gimpyfac

Member
Does all NM runs through the top and bottom plate need to have approved firestopped method to maintain the fire resistance rating,also attached garage, 5/8 drywall does boxes back to back using NM cable have to be kept 24" horizonatal.They can't be in the same hollow space?
 

drg

Senior Member
Re: fire stopping

Check out article 300.21 and the fpn.
Also some state and local jurisdictions might require that all penetrations weather fire rated or not be sealed so you probaly want to check for your area.


John
:)
 
A

a.wayne3@verizon.net

Guest
Re: fire stopping

Is this in a S.F.R.?????? If so then all that is needed is fire caulking at the top plate.Back to back in same cavity is fine.But is in a M.F.D,then that is a whole new animal !!!!!!
 
A

a.wayne3@verizon.net

Guest
Re: fire stopping

Agreed but the 5/8 drywall threw me off
 

pierre

Senior Member
Re: fire stopping

The firestopping requirement in the NEC has had the same section number since at least the '62 code cycle. I am told the reason it was not enforced until a few years ago is there were no listed products for the purpose.
The residential building code is very specific in the requirements for firestopping.

Pierre
 