  1. Replies
    35$$
    Views
    363

    We can all see the absurdity of it all. I wrote...

    We can all see the absurdity of it all. I wrote a proposal about septic pumps with alarms The units required 2 circuits however there was one structure.

    The cmp stated that the circuits were...
  2. Replies
    3$$
    Views
    38

    IMO, it is unclear in the nec. This is an...

    IMO, it is unclear in the nec. This is an authority having jurisdiction call referencing 334.15(B) In general if the romex follows a surface but is on the side of a stud, for instance, then it is...
  3. Replies
    4$$
    Views
    49

    To clarify you don't even have to have the...

    To clarify you don't even have to have the receptacles on the same circuit. They can come off any other circuit you wish
  4. Replies
    4$$
    Views
    49

    The only rule that I know about for commercial...

    The only rule that I know about for commercial baths is that if you install a receptacle then it must be gfci. Tje residential rule that you alluded to does not come into play
  5. Replies
    7$$
    Views
    535

    sorry $6.00 each

    sorry $6.00 each
  6. Replies
    7$$
    Views
    535

    LED prices have dropped considerably. We have...

    LED prices have dropped considerably. We have been using Philips bulbs and the R30 10.5 watt bulbs have come down from $30 or so to $12. Our poco is offering incredible deals to customers but we...
  7. Replies
    4$$
    Views
    64

    My guess is to use art. 440 or perhaps the...

    My guess is to use art. 440 or perhaps the nameplate.
  8. Replies
    4$$
    Views
    64

    From Wikipedia Vulcanization - Wikipedia, the...

    From Wikipedia
    Vulcanization - Wikipedia, the free encyclopedia



    Vulcanization (or vulcanisation) is a chemical process for converting natural rubber or related polymers into more durable...
  9. Replies
    10$$
    Views
    349

    I believe that is what Iron Ben was stating in...

    I believe that is what Iron Ben was stating in the above post
  10. Replies
    7$$
    Views
    183

    As others have said if the generator is properly...

    As others have said if the generator is properly wired and there is some phantom voltage present, then that is not the cause as phantom voltage will not be capable energizing equipment.
  11. Replies
    27$$
    Views
    541

    This whole thread sounds bogus. 9 gang cover...

    This whole thread sounds bogus.

    9 gang cover for a screen porch?

    9 gang box near the floor for Receptacles?

    Come on-- why would anyone do this. If it is for switches it still outrageous...
  12. Replies
    24$$
    Views
    490

    Seriously, if kmart sells batteries in the tool...

    Seriously, if kmart sells batteries in the tool section is it a tool. If the batteries are sold in the appliance center does that make it an appliance.

    Fiona, I am not sure what is going on...
  13. Replies
    24$$
    Views
    490

    IMO, a ceiling fan is not what is referred to in...

    IMO, a ceiling fan is not what is referred to in (G). It refers to art. 422. Look at 422.11(G)-- I don't think the fan qualifies. Why not just use #12 and be right.
  14. Replies
    24$$
    Views
    490

    Again de-rating etc has nothing to do with this. ...

    Again de-rating etc has nothing to do with this. You cannot use a 20 amp overcurrent protective device for 14 wire even at 90C. Can you show me where in the NEC it is allowed other than T240.4(G)?...
  15. Replies
    25$$
    Views
    605

    Generally I have used a surface recep. and turned...

    Generally I have used a surface recep. and turned it sideways and I have not had an issue. Personally I would wait for the unit to get there to be safe
  16. Replies
    19$$
    Views
    340

    Here is the article

    Here is the article
  17. Replies
    24$$
    Views
    490

    Fiona, all the calculations that you are doing is...

    Fiona, all the calculations that you are doing is insignificant. Start with 110.14(C). Then go to 240.4 and then table 310.16. Now look at the asterisk next to conductors 18, 16, 14, 12 and 10 and...
  18. Replies
    24$$
    Views
    490

    At one point you said 14/2 so I assume that is nm...

    At one point you said 14/2 so I assume that is nm cable. Regardless you cannot use overcurrent protective device at 90C since the breaker is only rated 75C

    Also art. 240.4 limits 14 wire to...
  19. Replies
    24$$
    Views
    490

    you cannot protect a 14 gauge conductor at 20...

    you cannot protect a 14 gauge conductor at 20 amps. I stated the article. The load on the wire is irrelevant. Put a 15 amp breaker and you will be compliant. art. 334.80, I think, for nm states...
  20. Replies
    24$$
    Views
    490

    14 only has an ampacity of 25 amps for de-rating....

    14 only has an ampacity of 25 amps for de-rating. NM cable is rated 60C and art. 240.4(D)(3) requires a 15 amp circuit except for special condition in (G)
  21. Replies
    24$$
    Views
    490

    How did that get approved with a 20 amp circuit? ...

    How did that get approved with a 20 amp circuit? This is not compliant.

    Not sure how you can control this. It would be easier if there were 4 switch legs instead of one. :D
  22. Replies
    1$$
    Views
    109

    They do make speed controls that will control 2...

    They do make speed controls that will control 2 fans but I will guarantee there will be a hum. If you can get someone to separate the fans.

    I am closing this thread, in accordance with the Forum...
  23. Replies
    24$$
    Views
    490

    Do I understand you that you have a 20 amp...

    Do I understand you that you have a 20 amp circuit with 14 gauge switch leg? I t also seems like you have one switch leg for all the fans, yes?
  24. Replies
    3$$
    Views
    158

    can you see what brand is there. I am sure there...

    can you see what brand is there. I am sure there are 24v lights available
  25. Replies
    22$$
    Views
    452

    I have heard of inspectors who turned down jobs...

    I have heard of inspectors who turned down jobs because of that. Easy fix-- put a tag on it.