  1. The CT in the meter, or the current coil in a...

    The CT in the meter, or the current coil in a series connected meter, will always detect current, but they will include the timing information as well, so that the meter can record the vector product...
  2. Replies
    10$$
    Views
    196

    If the 100A subpanel has a 100A main breaker it...

    If the 100A subpanel has a 100A main breaker it would be OK, yes?
    The "directly from to" statement is unclear. I do not Dee it as saying from a 200 main (service disconnect?) to a 200 main in...
  3. Thread: Induction

    by GoldDigger
    Replies
    1$$
    Views
    58

    There will be no inductive heating, since that...

    There will be no inductive heating, since that only occurs as the result of a changing magnetic field from AC current flowing through the wire. And only if the EMT or IMT or rigid is ferromagnetic...
  4. Replies
    13$$
    Views
    249

    I would see it as more likely that an unloaded...

    I would see it as more likely that an unloaded 200A wire would carry more heat away from a fully loaded or overloaded 100A wire, reducing the terminal temperature.
    The combination of fully loaded...
  5. Replies
    81$$
    Views
    1,952

    If a woodchuck could chuck all the wood he would...

    If a woodchuck could chuck all the wood he would chuck,
    how much wood would a woodchuck chuck?

    He'd chuck all the wood that a woodchuck could,
    if a woodchuck could chuck wood.
  6. Replies
    7$$
    Views
    240

    There are timers that will turn the fan on with a...

    There are timers that will turn the fan on with a light and then keep it on for an adjustable time delay after the light is turned off.
  7. Yes, I meant line to neutral voltages. The...

    Yes, I meant line to neutral voltages.
    The problem is that the common meter measures both line currents and assumes that each current corresponds to one half of the line to line voltage. The...
  8. Replies
    12$$
    Views
    348

    The NEC does not recognize the running (constant...

    The NEC does not recognize the running (constant diameter) threads of the connector as a fit for the tapered pipe threads of the LB.
    Unless it has somehow been listed for that specific use.
  9. Replies
    12$$
    Views
    348

    I think that it was a reference to a metallic...

    I think that it was a reference to a metallic raceway connection in addition to a ground/neutral bond at each end?

    Although I don't think anything in the OP implied bonding at each end, except...
  10. Replies
    16$$
    Views
    282

    The thing that hurts my head the most is the...

    The thing that hurts my head the most is the realization that even with all I have learned, here and elsewhere, I still, deep in my gut, feel that a ground electrode and GEC right at the shed is...
  11. Be very careful to note that the designation of...

    Be very careful to note that the designation of Minor Repair Garage states
  12. Replies
    19$$
    Views
    596

    Every water feature that I have seen uses a...

    Every water feature that I have seen uses a continuously running pump. But probably not very large.
    My pond uses a very large appearing 1/8 horse motor, since the flow and head are rather small....
  13. Replies
    16$$
    Views
    282

    See PS and PPS in my post. We crossed in the...

    See PS and PPS in my post. We crossed in the night. :)
  14. Replies
    16$$
    Views
    282

    In particular, (1) requires a GEC connection next...

    In particular, (1) requires a GEC connection next to the service disconnect, and if my interpretation is correct each shed has its own service disconnect.
    PS: But, looking more closely at the exact...
  15. Replies
    6$$
    Views
    123

    In particular, I suspect they are worried about...

    In particular, I suspect they are worried about double tapping lugs or otherwise doing stupid things, but instead of inspecting for that they have gone all formal on you.
  16. Replies
    19$$
    Views
    400

    I used to say that it is relatively easy to make...

    I used to say that it is relatively easy to make something idiot proof, much harder to make it engineer proof and impossible to make it physicist proof.
  17. Replies
    7$$
    Views
    163

    I am confused. It sounds like this is supplied...

    I am confused. It sounds like this is supplied from the same POCO service, which is a grounded wye. So the delta circuit that they run from that point outward is not going to be either ungrounded or...
  18. Replies
    16$$
    Views
    282

    The OP describes the shed wires as being...

    The OP describes the shed wires as being connected in the wireway next to the meter, and presumably upstream of the existing disconnects.
    That would make the shed wiring service conductors, which...
  19. Replies
    11$$
    Views
    317

    Been there. Learned nothing unexpected. For...

    Been there. Learned nothing unexpected.
    For residential use it is a total swindle.
    For commercial use if POCO charges a low PF penalty it might actually eventually pay for itself. But it will...
  20. Well, just about everyone tries, just in case the...

    Well, just about everyone tries, just in case the injured party does not have a lawyer.
  21. Replies
    81$$
    Views
    1,952

    Well, the instantaneous peak power every half...

    Well, the instantaneous peak power every half cycle will be twice the average power, even for a constant resistive load, so you technically need to specify some time period.
    I can also just see a...
  22. Replies
    7$$
    Views
    198

    I am beginning to see a pattern here too. :)

    I am beginning to see a pattern here too. :)
  23. Replies
    81$$
    Views
    1,952

    Whether it is based on kWh in a 15 minute period...

    Whether it is based on kWh in a 15 minute period or the average kW over that same 15 minutes, the practical effect is identical.
    Once you set a time period energy is directly proportional to average...
  24. Replies
    15$$
    Views
    499

    Detecting the condition when you have an EGC or...

    Detecting the condition when you have an EGC or other ground (even capacitive) available is not difficult. I think that the underlying question is why the furnace cares?
    It has been suggested that...
  25. Replies
    12$$
    Views
    301

    For a GES which includes building steel, water...

    For a GES which includes building steel, water pipes, a CEE or other electrodes that are distributed over a wide area, the fall of potential test can very hard to do properly. The shape and gradient...