  1. Replies
    1$$
    Views
    104

    Yes, if by "100 amp main service" you mean the...

    Yes, if by "100 amp main service" you mean the OCPD associated with the service disconnecting means is rated 100A.
  2. Replies
    7$$
    Views
    110

    I considered that premise, but nothing really...

    I considered that premise, but nothing really says you can't calculate the service/feeder load at the higher value.
  3. Replies
    7$$
    Views
    110

    I agree that you can. The question is will you?...

    I agree that you can. The question is will you?

    I don't find it odd because the service/feeder load calculation would not end up less than the branch circuit load sum. I'd find it odd if it were...
  4. Replies
    8$$
    Views
    153

    I second using of duct seal.

    I second using of duct seal.
  5. Replies
    48$$
    Views
    922

    Hmmm... po ta to po tah to :p 110.14(C)...

    Hmmm...

    po ta to
    po tah to

    :p

    110.14(C) doesn't say the circuit ampacity is limited to the terminal temperature limitation. Only 310.15(B) says that.
  6. Replies
    5$$
    Views
    153

    Essentially correct, but going to add some notes...

    Essentially correct, but going to add some notes for clarification.

    GEC's can be connected at any point along the service entrance neutral conductor. FWIW, some POCO's prohibit connections in the...
  7. Replies
    48$$
    Views
    922

    No need to bow out. ;) Your assessment is...

    No need to bow out. ;)

    Your assessment is correct (see my reply to David).

    An indirectly associated matter which I question is circuit rating being based on the OCPD rating (210.3), when the...
  8. Replies
    48$$
    Views
    922

    Okay... I've been having a hopefully momentary...

    Okay... I've been having a hopefully momentary lapse of reasoning today, and needed the reassurance. Thank you for your assistance in that regard. :happyyes:

    When I answered...

    ...I was...
  9. Replies
    5$$
    Views
    153

    Yes, but it will not be the service disconnecting...

    Yes, but it will not be the service disconnecting means, so you cannot land any GEC's there, nor can the neutral and grounding conductors, buses, enclosure be bonded.
  10. Replies
    48$$
    Views
    922

    But the conductor's [actual] ampacity is 75A.

    But the conductor's [actual] ampacity is 75A.
  11. Replies
    48$$
    Views
    922

    As electrofelon asked me, are you sure? (IMO)...

    As electrofelon asked me, are you sure?

    (IMO) Breaker rating has no bearing on meeting the terminal temperature limitation. That is solely determined by load (NC+125%C). In the example...
  12. Replies
    8$$
    Views
    202

    Depends on how you want to run it. Note in my...

    Depends on how you want to run it. Note in my first reply both cable tray methods have an ampacity over 650A. And the two conduit method has an ampacity over 600A. 240.4(B) permits the next higher...
  13. Replies
    48$$
    Views
    922

    No to one of 'em. :angel:

    No to one of 'em. :angel:
  14. Replies
    8$$
    Views
    202

    Correct. But I now have to throw in the 'bone...

    Correct.

    But I now have to throw in the 'bone us'. You have to do the actual ampacity calculation because the conductor must be protected at its ampacity by the OCPD (breaker/fuse). That's why my...
  15. No and yes, respectively.

    No and yes, respectively.
  16. Replies
    9$$
    Views
    139

    You could have reduced that to: ...

    You could have reduced that to:

    (600*240*3)/(480*1.732)=519.6A

    :)
  17. Replies
    8$$
    Views
    202

    Factoring continuous 125% is for determining...

    Factoring continuous 125% is for determining minimum SIZE conductor. You do not factor continuous when sizing for AMPACITY.


    Even if the equipment has 90°C terminations, it is quite likely the...
  18. Replies
    8$$
    Views
    202

    Assuming copper, 75°C terminations, 90°C rated...

    Assuming copper, 75°C terminations, 90°C rated conductors...

    SIZE:
    Parallel... 520A × 125% = 650A... ÷ 2 = 325A... 2 sets 400kcmil @ 75°C, 335A each, minimum.

    AMPACITY:

    (1) Conduit... 520A...
  19. Replies
    1$$
    Views
    84

    If you're doing this offset with a hydraulic...

    If you're doing this offset with a hydraulic bender, which, and what is the shoe's bend radius?

    Each bender will have minimum adjacent straight section requirements, e.g. distance to hook-end or...
  20. Replies
    8$$
    Views
    180

    Works for me to say it's a violation. :happyyes:

    Works for me to say it's a violation. :happyyes:
  21. Replies
    8$$
    Views
    180

    Hmm... sounds like the mobile home has a split...

    Hmm... sounds like the mobile home has a split bus panel... which means it's not parallel fed. Make any difference?
  22. Replies
    4$$
    Views
    121

    I was thinking .85 being a more reasonable...

    I was thinking .85 being a more reasonable estimate, but I have no solid basis, just a SWAG.

    Is there a purpose?
  23. Replies
    9$$
    Views
    139

    Doesn't change anything.

    Doesn't change anything.
  24. Replies
    19$$
    Views
    315

    Shouldn't as long as it is solidly connected to...

    Shouldn't as long as it is solidly connected to the power supply grounding conductor.
  25. Replies
    9$$
    Views
    139

    Yes (Sorry I edited my post but it amounts to...

    Yes

    (Sorry I edited my post but it amounts to same info)