  1. Replies
    14$$
    Views
    572

    I couldn't agree more unless were running...

    I couldn't agree more unless were running strictly MC cable to concealed panels (probably not an issue for you). :D

    We have in the past ordered KO's only on one end of the panel so you could use...
  2. Replies
    16$$
    Views
    295

    A multi-wire branch circuit on a 2 pole CB can...

    A multi-wire branch circuit on a 2 pole CB can also be 2 circuits. If I run a three wire cable (MWBC) to the kitchen counter and feed two different receptacles I would have met the minimum 2 circuit...
  3. Replies
    16$$
    Views
    295

    If it's a single pole circuit breaker it's only...

    If it's a single pole circuit breaker it's only one circuit. The loads connected do not matter.
  4. Replies
    16$$
    Views
    295

    The question stinks but I would go with the...

    The question stinks but I would go with the simplest answer which would be 1. Technically it could be 1, 2, or 3 if you had a 1 pole, 2 pole or 3 pole CB.

    Welcome to the forum.
  5. Replies
    14$$
    Views
    303

    eBay $16. ...

    eBay $16.

    http://www.ebay.com/itm/Cable-Hammer-Crimper-Tool-Battery-Welding-Wire-Terminal-Lug-Connector-8-4-0-AWG-/132074169267
  6. Replies
    14$$
    Views
    303

    Yes, this would be for #4 AWG battery cables on a...

    Yes, this would be for #4 AWG battery cables on a boat.
  7. Replies
    3$$
    Views
    138

    So you're feeding the exterior surface mounted...

    So you're feeding the exterior surface mounted subpanel with NM cable entering directly into the back? Sounds fine to me, no different than entering the back of an FS box.
  8. Replies
    14$$
    Views
    303

    I've read some reviews for similar products and...

    I've read some reviews for similar products and people say that they actually work. For less than $20 it might be worth it.
  9. Replies
    14$$
    Views
    303

    Cable Hammer Crimper Tool

    Has anyone ever used one of these for a few crimps? I need to make two crimps on some boat cables and don't feel like dragging the heavy Burndy battery crimper all the way from the job to the...
  10. Replies
    12$$
    Views
    284

    I would assume that it was silver plated unless...

    I would assume that it was silver plated unless told otherwise.
  11. Replies
    1$$
    Views
    139

    Just listed for damp locations.

    Just listed for damp locations.
  12. Replies
    7$$
    Views
    267

    250.118 lists equipment grounding conductors and...

    250.118 lists equipment grounding conductors and RMC is on the list so there is no code issue with your installation.
  13. Replies
    14$$
    Views
    572

    I agree with you, many of them are terrible to...

    I agree with you, many of them are terrible to remove. Often I will bend them slightly and then cut each section of the concentric ring with my dykes to isolate one little tab at a time. The...
  14. Replies
    7$$
    Views
    267

    Is there a metallic conduit feeding the panel? ...

    Is there a metallic conduit feeding the panel? If is it may be fine as is.
  15. Replies
    2$$
    Views
    122

    The ground fault protection in the service can...

    The ground fault protection in the service can protect the downstream equipment. Redundant protection is not required.
  16. Replies
    4$$
    Views
    195

    You would hard pressed to find any residential...

    You would hard pressed to find any residential panelboards that have lugs rated for two conductors. IMO it's safe to assume that if you find two conductors under such a terminal it's a violation.
  17. Replies
    12$$
    Views
    516

    I would go with the separate service option since...

    I would go with the separate service option since it sounds like you don't want to add a big load to the existing service which also may keep them from needing to upgrade the existing service in the...
  18. Replies
    2$$
    Views
    186

    You can use just the raceway of it qualifies as a...

    You can use just the raceway of it qualifies as a EGC.
  19. Replies
    4$$
    Views
    296

    Is there any gear with exposed live parts?

    Is there any gear with exposed live parts?
  20. Replies
    16$$
    Views
    848

    Mostly AC which runs about $400/month during the...

    Mostly AC which runs about $400/month during the middle of the summer. Electric rates are pretty high in the Northeast.
  21. Replies
    11$$
    Views
    590

    If you look at the section Roger posted it will...

    If you look at the section Roger posted it will tell you that flat cables are calculated as if they were round using it's widest dimension.
  22. Replies
    16$$
    Views
    848

    Natural gas around here is super cheap,...

    Natural gas around here is super cheap, electricity super expensive. My natural gas monthly budget plan is $53/month or $636.00 per year. That's for heat, hot water, gas range, gas dryer and gas...
  23. Replies
    9$$
    Views
    509

    The NEC does not prohibit the continued use of...

    The NEC does not prohibit the continued use of rubber insulated conductors. Even knob and tube is still permitted.
  24. Replies
    7$$
    Views
    298

    I concur with the others, flush with the floor is...

    I concur with the others, flush with the floor is not a problem and conductive not a problem.
  25. Replies
    1$$
    Views
    179

    Take a look at 620.11(B).

    Take a look at 620.11(B).