  1. Have the NEC take action and eliminate art....

    Have the NEC take action and eliminate art. 310.3(A)(3) as I proposed this year. This section allows NM to be run in a manner that electromagnetic field's will be present.
  2. I would advise you to not share a neutral with an...

    I would advise you to not share a neutral with an afci. Unless you use GE afci breakers you would need a dp afci not 2 sp breakers with handle ties- that will not work.
  3. Replies
    11$$
    Views
    135

    When I said black pipe I meant CSST piping that...

    When I said black pipe I meant CSST piping that is black-- that is the counter strike which does not require additional bonding but then if local codes require it to be bonding the manufacturer then...
  4. Maybe I'll sue the mobile companies because I got...

    Maybe I'll sue the mobile companies because I got Multiple Myeloma from the air waves. You know, I never felt the same once I started using the phones. :D
  5. Replies
    11$$
    Views
    135

    This is from Omegaflex

    This is from Omegaflex
  6. Replies
    11$$
    Views
    135

    Of course the black "Counter strike" made by...

    Of course the black "Counter strike" made by omegaflex does not require any bondng
  7. Replies
    11$$
    Views
    135

    Not all pipe manufacturers require #6. I believe...

    Not all pipe manufacturers require #6. I believe Omegaflex used to require the use of T. 250.66-- I assume it still does but it has been awhile since I have checked.
  8. Replies
    11$$
    Views
    135

    What size service is it? A 200 amp service will...

    What size service is it? A 200 amp service will need a #4 to bond the gas pipe so connecting to the #6 will not be compliant
  9. There has been so many things cited that cause...

    There has been so many things cited that cause Autism. Unfortunately there is no scientific evidence, IMO that supports any of these. Like every thing in life there are the believers and non...
  10. You're welcome. Here is something else to...

    You're welcome. Here is something else to understand-- Causes of electromagnetic field due to wiring
  11. Replies
    3$$
    Views
    161

    I agree with Bob however I want to clarify that...

    I agree with Bob however I want to clarify that if the loads are continuous then you cannot load the panel to 100 amps unless the breaker feeding the panel is listed at 100%. I doubt there are any...
  12. Replies
    10$$
    Views
    271

    Yes there will be 120v on the tombstones and yes...

    Yes there will be 120v on the tombstones and yes they make LED lamps that replace the fluorescent but the fixture must have an electronic ballast not the magnetic ones from the T12 fixtures. At...
  13. If that is the health standard I am surprised. I...

    If that is the health standard I am surprised. I was told anything higher than 4 miligauss is unsafe. Ohers have said 8 mgauss. I have never heard of 833 mgauss as being the standard. That is...
  14. Replies
    16$$
    Views
    380

    The meter is not the issue with a window. It has...

    The meter is not the issue with a window. It has to do with the service drop and drip loop not the base itself.
  15. Replies
    3$$
    Views
    95

    Look at the Table again. It states size not...

    Look at the Table again. It states size not exceeding a size. If the overcurrent protective device is more than 100 amps and less than 200 amps then you use the 200 amp column. Thus #4 aluminum is...
  16. Thank you for the confidence in me. As winnie...

    Thank you for the confidence in me. As winnie stated Karl is the expert but he has not been active here for quite awhile. I am still learning and it seems every now and then I find out new info. I...
  17. Replies
    4$$
    Views
    121

    So the service is mounted on a separate structure...

    So the service is mounted on a separate structure from the building? You still need to follow 225.32 however I see some issues here as a structure may only be fed with one feeder-- 225.30. Maybe...
  18. IMO, mc cable or conduit will reduce any...

    IMO, mc cable or conduit will reduce any electromagnetic field's. Depending on the sensitivity of the individual you could get by with NM cable. I know that we are being told we must use mc in a...
  19. Replies
    4$$
    Views
    121

    IMO, the disconnects will have to be grouped at...

    IMO, the disconnects will have to be grouped at the service --230.72 and then it may be allowed to be mlo panels in each unit but that would depend on whether the units are separated by firewalls.
  20. Replies
    15$$
    Views
    357

    I just want to state that the pipe work is...

    I just want to state that the pipe work is beautiful. Nice job - congrats to whoever did this work.
  21. Replies
    1$$
    Views
    157

    IMO, yes for both as long as the motor is...

    IMO, yes for both as long as the motor is protected properly.
  22. Replies
    2$$
    Views
    122

    I feel that is about all we can help you with...

    I feel that is about all we can help you with this issue so I will have to close this thread based on our rules.

    I am closing this thread, in accordance with the Forum Rules.

    If you feel this...
  23. Replies
    2$$
    Views
    122

    Chris I am not sure what we can do without...

    Chris I am not sure what we can do without knowing all the info. It does sound like either a bad breaker or a bad wire in the ground. It has nothing to do with the 200 amp panel being fed from a 100...
  24. Replies
    10$$
    Views
    271

    I think the 120V led bulb that replaces a 4'...

    I think the 120V led bulb that replaces a 4' fluorescent - no ballast involved cost about $30 each
  25. Replies
    18$$
    Views
    523

    I agree with the 2 doors on one 20 amp circuit...

    I agree with the 2 doors on one 20 amp circuit and the rest can be on another circuit but I would use 20 amps on that also. I would also put the lights on another 15 amp circuit especially if there...
Results 1 to 25 of 200