  1. Only some designs of drains let all of the water...

    Only some designs of drains let all of the water out of the enclosure. Other designs leave an 1/8" of more of water in the bottom of the enclosure.
  2. How is 770.3 and 770.110(A)(1) not a conflict.

    How is 770.3 and 770.110(A)(1) not a conflict.
  3. Replies
    9$$
    Views
    102

    Neither the main rule nor that exception are...

    Neither the main rule nor that exception are needed in the code. The combination puts us right back where we were before there was a rule that said you can't use the EGC as a GEC. With the...
  4. Replies
    29$$
    Views
    580

    What type of jacket does the multi-conductor...

    What type of jacket does the multi-conductor cable have? If the cable has a magnetic jacket, then all of the circuit conductors and the EGC have to be within that jacket, and if the cables are in...
  5. In my opinion it is.

    In my opinion it is.
  6. Replies
    13$$
    Views
    633

    As far as I know the wire pulling calculations...

    As far as I know the wire pulling calculations assume a NEC compliant bend radius.
  7. Replies
    7$$
    Views
    223

    It is my opinion that 725.136(I) permits the...

    It is my opinion that 725.136(I) permits the installation without any type of barrier. Since there is no specific subsection that covers the two systems within a raceway, it appears to me that "(I)...
  8. Replies
    13$$
    Views
    633

    Note that the pulling tension calculator does not...

    Note that the pulling tension calculator does not have an input for the radius of the bend for calculating the tension or pulling force. The radius is only used for the sidewall pressure calculation.
  9. Replies
    7$$
    Views
    223

    Exception #1, in most cases, permits installation...

    Exception #1, in most cases, permits installation with no separation between the power and communication cables. Other standards require separation, but they are base on system performance and the...
  10. Replies
    29$$
    Views
    580

    I guess I need to retract my statement based on...

    I guess I need to retract my statement based on 300.3(B)(3). That would clearly apply to the NM and may apply to the cable in the cable tray based on that cable having a nonmagnetic jacket.
  11. Replies
    29$$
    Views
    580

    It is my opinion that you can only do that where...

    It is my opinion that you can only do that where you are installing single conductors in the cable tray. If you are installing a multi-conductor cable, you need an EGC in each cable.
  12. Replies
    29$$
    Views
    580

    It would be my opinion that neither one is code...

    It would be my opinion that neither one is code compliant. If you have a cable assembly the EGC must be part of that cable assembly. It cannot be run external.
  13. Replies
    7$$
    Views
    379

    Have you checked the prices of stainless supports...

    Have you checked the prices of stainless supports compared to PVC coated supports?
  14. Replies
    45$$
    Views
    995

    The water piping bonding rule does not use that...

    The water piping bonding rule does not use that phrase. Water piping [250.104(A)]systems are required to be bonded even where it is not likely to become energized. Other piping systems...
  15. Replies
    45$$
    Views
    995

    The plumbing connections between the piping and...

    The plumbing connections between the piping and between the piping systems, assuming metallic faucet bodies is sufficient for the code required bonding.

    Maybe you don't we do around here and in...
  16. Replies
    4$$
    Views
    158

    Mike always says it takes three cycles to get a...

    Mike always says it takes three cycles to get a code change correct!
  17. The requirement for the supply side bonding...

    The requirement for the supply side bonding jumper is the same no matter where the system bonding jumper is installed.
  18. Replies
    7$$
    Views
    379

    Sometimes.

    Sometimes.
  19. Replies
    20$$
    Views
    481

    Not according to federal law.

    Not according to federal law.
  20. Replies
    45$$
    Views
    995

    Mike, It is not about what those definitions...

    Mike,
    It is not about what those definitions say, it is about the physics of the connection, and the physics does not change just because we call one metallic connection part of the water piping...
  21. Replies
    45$$
    Views
    995

    It doesn't matter what they are a part of...a...

    It doesn't matter what they are a part of...a screwed joint on the pipe itself is not any different from a srewed connection to a metallic faucet body. If you are saying that the metallic faucet...
  22. Replies
    45$$
    Views
    995

    So based on that reasoning, you must also require...

    So based on that reasoning, you must also require a bonding jumper at each and ever joint in the water piping system. Pipe joints are not designed or tested as a fault clearing path.
  23. You can view all of the NFPA documents at...

    You can view all of the NFPA documents at www.nfpa.org. They are not in the most user friendly format, but they are viewable.
  24. Replies
    7$$
    Views
    379

    If you really needed the PVC coated rigid and you...

    If you really needed the PVC coated rigid and you install it with non-coated hangers, the conduit won't remain in place very long....the hangers will corrode away.
  25. Replies
    2$$
    Views
    171

    See 225.18.

    See 225.18.