  1. 210.23(A)(2) is not violated unless fixed...

    210.23(A)(2) is not violated unless fixed utilization equipment is connected to the same circuit and any single fixed utilization equipment exceeds 50% of the circuit rating.

    422.16(B)(4) requires...
  2. I he is just questioning why he reads 115.7 volts...

    I he is just questioning why he reads 115.7 volts instead of 114 if the primary voltage is 456.

    The alarm issue is under voltage not over voltage from what I can tell, and apparently it is...
  3. Replies
    2$$
    Views
    63

    Usually rated for full 5 amps, but often they...

    Usually rated for full 5 amps, but often they will say X amps (inductive), X amps (resistive) so type of load supplied needs consideration. Some contacts may have a tungsten filament rating as well.
  4. Replies
    3$$
    Views
    95

    I think the OP should not have called it a SO...

    I think the OP should not have called it a SO cable early in the post. The product he referred to at the end of the post is not your general use type SO flexible cord.

    What little information I...
  5. Replies
    5$$
    Views
    166

    To add to what you said - once you are past the...

    To add to what you said - once you are past the main or system bonding jumper location, the "grounded (most often is a neutral)" and "equipment grounding" conductors must be kept separated from one...
  6. Replies
    4$$
    Views
    156

    I'm not too concerned about the need for a fire...

    I'm not too concerned about the need for a fire extinguisher, but is funny.

    too small of a conductor just means an already low grade contactor or relay will fail even sooner if too small of a lead...
  7. Replies
    3$$
    Views
    127

    That is same application that I have run into in...

    That is same application that I have run into in the past where I have had inspectors wanting a rejection base installed.

    My problem is if you try to give a specific protection level to a...
  8. Have you measured voltage while normal loads are...

    Have you measured voltage while normal loads are operating?

    If you have a poor connection you may find it faster to find it if you apply a temporary heavy load and monitor voltage, 1000-1500 watt...
  9. Replies
    2$$
    Views
    66

    Was just talking about this article in the last...

    Was just talking about this article in the last thread I replied to, look at 210.23(A)(2). If they draw more then 50% of the branch circuit rating they can not have lighting or non fastened in place...
  10. It would have to be over 1800 watts to need more...

    It would have to be over 1800 watts to need more then a 15 amp circuit. I don't know if I have ever seen one over 1800 watts.

    I agree, on the stop enabling them. If they are a decent person they...
  11. I agree, but with a wind turbine we could have a...

    I agree, but with a wind turbine we could have a metal pole being used as a raceway for conductors - in that case I don't see an issue with using the pole as the EGC.
  12. Replies
    9$$
    Views
    348

    That was for removal my comment was on repairing...

    That was for removal my comment was on repairing what was in the OP, probably just needs a little cleaning to get it back to about the condition it was in before this incident.
  13. Replies
    6$$
    Views
    197

    Theoretically it should be carrying half the...

    Theoretically it should be carrying half the current of the complete set (of a set of 2) but I would clamp each one separately in case they are not balanced for some reason and consider the sum of...
  14. Thread: NAIL PLATES !

    by kwired
    Replies
    10$$
    Views
    329

    I see a problem, but not going to waste my time...

    I see a problem, but not going to waste my time on it either.

    It also doesn't effect how I intend to make my installs - they will still be 1-1/4 from the face of the framing member.
  15. Replies
    9$$
    Views
    348

    Wasn't by chance only metering 120 volts with a...

    Wasn't by chance only metering 120 volts with a 120 volt only meter being used?

    May have been necessary to not open the grounded conductor when pulling the meter because of some crossover in...
  16. Thread: NAIL PLATES !

    by kwired
    Replies
    10$$
    Views
    329

    But why make it more confusing with the word...

    But why make it more confusing with the word "wood" in the title of (A)? Why does 330.17 not include 300.4(B)? Seems about as pointless to me as having the word "wood" in the title of (A).

    I would...
  17. NEC doesn't apply to the components of a listed...

    NEC doesn't apply to the components of a listed piece of equipment, you need to look at what the listing requirements call for. Wiring running to/from your piece of equipment likely will be required...
  18. Replies
    9$$
    Views
    348

    No more then it cost to rent a power washer for a...

    No more then it cost to rent a power washer for a few hours. After that kind of treatement I'd guess it won't look much different then it did before this happened, other then it may still need some...
  19. Replies
    10$$
    Views
    309

    If it is an inexpensive pump, buy a new one if it...

    If it is an inexpensive pump, buy a new one if it is a higher priced pump, may be worth replacing seals if that is what has failed. If you won't or don't want to take on that challenge have them take...
  20. I guess next question is are you talking steel...

    I guess next question is are you talking steel structure of a building or steel structure of a listed piece of equipment that you may be making to ship to US.
  21. Replies
    7$$
    Views
    258

    I guess I did, I was trying to say it is not...

    I guess I did, I was trying to say it is not ordinarily a pediatric care area.

    A "waiting room" in a pediatric care wing or floor may or may not need TR receptacles, just like a surgery room in...
  22. Replies
    7$$
    Views
    258

    Not necessarily to a waiting room though. 2011...

    Not necessarily to a waiting room though.

    2011 says "rooms, bathrooms, playrooms, activity rooms, and patient care
    areas of designated pediatric locations"

    A waiting room is usually a place...
  23. Replies
    5$$
    Views
    225

    Not a NEC requirement. Not a bad design either,...

    Not a NEC requirement. Not a bad design either, especially in cases where strict LOTO practices are applied.
  24. Thread: 600 amp service

    by kwired
    Replies
    10$$
    Views
    278

    It will be, until it fails the inspection;) I...

    It will be, until it fails the inspection;)

    I know you corrected yourself already though.
  25. Thread: Legal splice ?

    by kwired
    Replies
    27$$
    Views
    727

    The live work rules are to protect the worker not...

    The live work rules are to protect the worker not the equipment.

    That said it is still more of a design decision then a code rule. Some panels (mostly the 1 inch wide interchangeable plug on...