    Probably what he was thinking of... but it does...

    Probably what he was thinking of... but it does not supersede 338.10(B)(4)(a).
  2. It is connected directly to the service portion...

    It is connected directly to the service portion of the system, correct? By definition, that makes it Service Equipment.
  3. It don't have to go anywhere beyond the...

    It don't have to go anywhere beyond the disconnect...




    Yep. You're not on the load side of a service disconnecting means, so you ground/bond to the service grounded conductor.
  4. Sorry for being late to the discussion. I've...

    Sorry for being late to the discussion. I've been reading most of the posts as it progressed but too busy to post myself...

    Neither.

    First, there are no paralleling rules for GECs. To be in...
  5. Replies
    5$$
    Views
    235

    I'm leaning this way myself. 22A x sqrt(3) =...

    I'm leaning this way myself. 22A x sqrt(3) = 38A. The nameplate (or spec's) say 36, so there could be a small load across the otherwise open end of the delta configuration... or if 4-wire, some...
  6. Replies
    16$$
    Views
    298

    I'd say every AHJ would approve that as...

    I'd say every AHJ would approve that as engineering supervision.
  7. Replies
    9$$
    Views
    211

    Best if OP'er provides product make and model, or...

    Best if OP'er provides product make and model, or better yet, links to their documentation.
  8. Replies
    9$$
    Views
    221

    As noted... but looking at it the other way...

    As noted... but looking at it the other way around

    800A or less OCPD rating, the conductor ampacity value has to be greater than the next lower standard OCPD rating value.

    Over 800A OCPD, the...
  9. Replies
    30$$
    Views
    664

    No state level in Ohio, but yearly for several...

    No state level in Ohio, but yearly for several local municipalities.
  10. I think we're well past that possibility. :D

    I think we're well past that possibility. :D
  11. 800A and less, yes. 215.2 for minimum feeder...

    800A and less, yes. 215.2 for minimum feeder conductor size. 215.3 for minimum feeder conductor OCPD.
  12. Replies
    7$$
    Views
    222

    If your rods are outside, just bond to the...

    If your rods are outside, just bond to the grounded neutral conductor in the CT cabinet. As far as bonding the utility conduits and CT to panel nipples, I prefer to just use bonding locknuts... no...
  13. Replies
    9$$
    Views
    387

    Yes... and any other breaker in the MLO panel is...

    Yes... and any other breaker in the MLO panel is also a service disconnecting means (or a disconnect for equipment permitted to be connected on the line side of service disconnecting means per...
  14. I agree with your assessment.

    I agree with your assessment.
  15. I have to wonder how you're going to run a ground...

    I have to wonder how you're going to run a ground ring just around the expansion. To qualify as a ground ring, it has to run around the entire building. EVen if you manage to do this just for the...
  16. Specifically in this case, being MTM, 225.30(A)...

    Specifically in this case, being MTM, 225.30(A) "Systems designed for connection to multiple sources of supply for the purpose of enhanced reliability".
  17. Noteworthy point. Perhaps one feeder then...

    Noteworthy point.


    Perhaps one feeder then tapped to supply the MCCs...???
  18. It's a better electrode and quite easy to install...

    It's a better electrode and quite easy to install provided you are there at the appropriate time. To install one rod will essentially require a second unless you due a bonafide ground resistance...
  19. Correct... other than where supplied by a branch...

    Correct... other than where supplied by a branch circuit.


    There is no requirement to connect back to the remote GES by way of a GEC or bonding jumper. The connection is made through the EGC run...
  20. Replies
    31$$
    Views
    1,064

    I'm hearing a lot of supposition here... but...

    I'm hearing a lot of supposition here... but rather than debating that, I'd like to point out a lot of what I'm hearing is based on the system actually being "earthed". While there is little reduced...
  21. Thread: Sanity Check

    by Smart $
    Replies
    3$$
    Views
    233

    For line-to-neutral loads, all the power (or...

    For line-to-neutral loads, all the power (or volt-amperes) goes on one leg.
    For line-to-line loads, half the power (or volt-amperes) goes on each leg.
    For 3-phase loads, one-third the power (or...
  22. Thread: torquing ques?

    by Smart $
    Replies
    6$$
    Views
    191

    It'd qualify for the torque tool part. I know...

    It'd qualify for the torque tool part.

    I know what "calibrated" means in the places I work, but to just put that term in there without some other criteria is going to initiate a fair amount of...
  23. Replies
    3$$
    Views
    151

    AFAIK comm cables are never required to be in a...

    AFAIK comm cables are never required to be in a raceway.
  24. Thread: torquing ques?

    by Smart $
    Replies
    6$$
    Views
    191

    Annex I

    Annex I
  25. Every building requires its own GES if it has any...

    Every building requires its own GES if it has any electrical equipment. The only exception is a residential outbuilding served by a single branch circuit. The NEC does not prohibit tying multiple...